I have some data in a Micro850, stored as a "WORD" datatype. I want my Control Logix to read that info. I know my MSG works, it will read INT values.
The MSG isn't happy when I point it at a WORD datatype. Do I need to add logic in the Micro850 to convert the WORD to an INT?

Thanks
Justin
 
What do you use WORD data types for in Micro 800 ? I don't use those controllers so I'm not familiar with that data type and how it differs from a UINT.

The Micro 800 CIP Client Messaging quick-start document suggests that your conclusion is correct, because it calls out the data types that are accessibly with a MSG instruction from a Logix family controller, though it doesn't specifically address the WORD data type.

From Appendix F:

Logix MSG instruction can read/write SINT, INT, DINT, LINT and REAL data types using “CIP Data Table Read” and “CIP Data Table Write” message types.

BOOL, USINT, UINT, UDINT, ULINT, LREAL, STRING, SHORT_STRING, DATE, and TIME data types are not accessible with the Logix MSG instruction.
 
I didn't write the code in the Micro850. One WORD is 16 BITS. In this machine, those BITS are alarms. I want my ControlLogix to read the WORD, haven't verified if it is possible or not yet.

word.PNG
 
It appears that the Micro800 reports the WORD type as UINT (0xc7). So I wonder if you have to declare a UINT in the ControlLogix to be able to read it? ControlLogix didn't add unsigned types until the 5580 platform (L8x) and firmware rev 32.
 

Similar Topics

I have a ControlLogix system, 5 processors w/ethernet and ControlNet over Devicenet. The processors are located in 4 racks and are remote from...
Replies
3
Views
6,272
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
132
Is there a way to use the FAL instruction to do +=2 instead of +=1? I have an array that is organized with alternating "data" and "flag" values...
Replies
5
Views
125
Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
Replies
3
Views
235
Hi Iam using monitouch hmi(V9 soft) with omron plc cj2m (CX programmer). In this I want to read a data from hmi to plc. The data was like...
Replies
0
Views
94
Back
Top Bottom