ControlLogix changing MSG Path Data issue

So first let me say I'm sure this is an easy one to solve but it's thrown me off today.
Background, I am using a single message instruction to read data out of 23 Powerflex 525's by changing the instance and IP address in the message path. This is not an unusual situation overall but I'm having an unusual issue.

For the record I've done this with Powerflex 40's on DeviceNet and Powerflex 753 over Ethernet before using the same fundamental logic and it's worked without issue.

The message Path is a String FYI. When trying to modify the message path in the tag at MessageName.Path.DATA[15] for example if I move a '4' in SINT format into that data location it ends up being '$04' instead.

This throws off my IP address and the message doesn't work due to communication errors. If I manually replace '$04' with a '4' in MessageName.Path.DATA[15] of the message tag it starts working right away.

What I'm trying to figure out is how to get the data moved without gaining the additional characters.

I should mention it's a Compactlogix L43 running revision 20.18 and the Powerflex 525 drives are at revision 5.1.

TIA.
  Reply With Quote
Old July 24th, 2017, 04:35 PM   #2
cwal61
Member
United States

cwal61 is offline
 
Join Date: Jan 2011
Location: NC
Posts: 981
try mov 52 into SINT MessageName.Path.DATA[15] 52 in decimal = '4'
  Reply With Quote
Old July 24th, 2017, 04:55 PM   #3
Dirtleg
Member
United States

Dirtleg is offline
 
Join Date: Dec 2014
Location: Virginia
Posts: 17
I see where you're going with this. I'll look into it tomorrow. Thank you for the different approach.
  Reply With Quote
Old July 24th, 2017, 04:56 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,293
You aren't "gaining additional characters", you're inadvertently substituting actual hex values for ASCII characters.

The PATH String is a combination of hex values and ASCII characters. In the case of a MSG going out to an Ethernet device, the first four SINT elements in the Path string data array are the CIP hops, after which comes the IP address in ASCII format.

My guess is that you're trying to change the last octet of the IP address.

The problem I've run into with this is when the last octet changes the number of digits, i.e. when I go from .9 to .10 or from .99 to .100.

That affects the Length element of the path String, and also changes the fourth byte of the path string itself, which describes the length of the ASCII parts of the array.

In ControlLogix, you can convert a DINT to a String with the DTOS instruction. If you move the characters created by that instruction into the part of the string for the last octet, and then correctly modify both the Path String .LEN and the path string's DATA[3] value, then your MESSAGE control data block changes should work.
  Reply With Quote
Old July 24th, 2017, 05:19 PM   #5
Dirtleg
Member
United States

Dirtleg is offline
 
Join Date: Dec 2014
Location: Virginia
Posts: 17
Thank you Ken.
I will admit I don't have much ASCII experience.
I tried using a DTOS earlier in the day with a CONCAT to create the IP address in string format and then copy that to DATA[3] but must have been messed up on the LEN.

I'll give your method a shot in the morning.
  Reply With Quote
Old July 24th, 2017, 06:51 PM   #6
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,407
Quote:
Originally Posted by Ken Roach View Post
You aren't "gaining additional characters", you're inadvertently substituting actual hex values for ASCII characters.

The PATH String is a combination of hex values and ASCII characters. In the case of a MSG going out to an Ethernet device, the first four SINT elements in the Path string data array are the CIP hops, after which comes the IP address in ASCII format.

My guess is that you're trying to change the last octet of the IP address.

The problem I've run into with this is when the last octet changes the number of digits, i.e. when I go from .9 to .10 or from .99 to .100.

That affects the Length element of the path String, and also changes the fourth byte of the path string itself, which describes the length of the ASCII parts of the array.

In ControlLogix, you can convert a DINT to a String with the DTOS instruction. If you move the characters created by that instruction into the part of the string for the last octet, and then correctly modify both the Path String .LEN and the path string's DATA[3] value, then your MESSAGE control data block changes should work.
Ken, I'm wondering if it would work if the path decimalised "octets" had leading zeroes?

e.g. "010.001.125.035" instead of "10.1.125.35"

That would make for easier substitution of the path in the MSG tag, without changing its overall length.

I can try this tomorrow and report back... it's way too late here to do it now.

Of course a simpler answer would be to re-address all the IP's to start at 100, i.e. 3 digits already, but that may be too big a challenge to even consider.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old July 24th, 2017, 07:08 PM   #7
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,293
This method frazzled me until I realized I have to account both for the total .LEN of the CIP Path as well as for the length of the IP Address string embedded in the CIP Path.

Here's a bit of logic that should work, but because I did it on a 1756-L71 you'll need to be sure your CIP Path to the 1768-ENBT and out onto Ethernet is similar.
Attached Images
File Type: jpg CIP_Path_Calculate.jpg (44.5 KB, 83 views)
  Reply With Quote
Old July 24th, 2017, 07:14 PM   #8
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,293
Dave,

If you ever want to see our in-house Unix guy turn a particular shade of University of Washington Department of Computer Science purple, show him that the ControlLogix OS doesn't interpret leading zeroes as octal, but the closely-related RSLinx Classic software does.

Poking the correct values into both the .LEN and the .DATA[x] location that holds the IP Address String works in this case.

For anything less than twenty devices I would recommend using individual MSG control tags. They don't take up that much space, and brute force can be elegant in its own way.

In my case, I had 120 identical devices and needed to direct the attention of some MSG instructions to just one of them at a time, so the manipulation of the CIP Path in a MSG instruction made sense.
  Reply With Quote
Old July 24th, 2017, 07:22 PM   #9
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 1,893
Good grief! Never thought one can dynamically change MSG path like that.

oh, Go Huskies!
  Reply With Quote
Old July 24th, 2017, 07:50 PM   #10
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,407
Quote:
Originally Posted by Ken Roach View Post
..... show him that the ControlLogix OS doesn't interpret leading zeroes as octal, but the closely-related RSLinx Classic software does.
OMG !! then you have to blame the choirmaster, not the choirboys... different song-sheets !

It reminds me of the time I discovered that JSR/SBR parameters are handled in the reverse order in SoftLogix, as opposed to "as specified" order for a hardware controller. It was a complete b@11$-up for our tried and tested "software standards"
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old July 25th, 2017, 09:00 AM   #11
Dirtleg
Member
United States

Dirtleg is offline
 
Join Date: Dec 2014
Location: Virginia
Posts: 17
Okay I got it. Probably just needed to sleep on it.

My mistake when using the DTOS to convert my DINT value to a string was that I wasn't selecting individual elements of the converted string when trying to insert them into the message path string.

For example, when I only need to change the last digit of the IP I copy String.DATA[0] into Message.Path.DATA[15] with a length of 1. If I need to change the last 2 digits of the IP I copy String.DATA[0] into Message.Path.DATA[14] with a length of 2. If all 3 need to be changed then it's the same but Path.DATA[13] and length of 3.
(disclaimer: depending on your particular setup the location of where you copy the data to may be different)

So now that that is sorted it works perfectly.

Thanks guys for helping me get out of my tunnel and look a little more broadly at this situation.
  Reply With Quote
Old July 25th, 2017, 11:33 AM   #12
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,293
About the "copy one character, or two, or three" issue:

That's what my snippet does with the FLL and COP instructions.

The FLL is to zero out any characters that are present after the last dot in the IP address string. A hexadecimal zero value = a "null" character in ASCII, so when I execute the FLL instruction, all the characters after the dot become null.

The COP instruction copies either one, two, or three characters because the source and the destination are both SINT[x] arrays. I used the .LEN value of the string I created with the DTOS as the LENGTH argument of the COPY instruction, because that's going to be 1, 2, or 3.
  Reply With Quote
Old July 25th, 2017, 10:02 PM   #13
bdjohns1
Member
United States

bdjohns1 is offline
 
Join Date: Sep 2006
Location: IL
Posts: 12
In the "there's more than one way to skin the cat" department, I had an OEM who was doing something similar - they needed to send a command to each of 16 Cognex cameras, located at 192.x.x.11-18, and 192.x.x.21-28.

They had a loop with a counter that would go from 1-8 , and then build their command string by adding either 10 or 20 to the loop counter, then a DTOS, then a CONCAT with a fixed string containing the CIP jumps and first 3 parts of the IP address, ending up putting that into the .Path parameter of the MSG.
  Reply With Quote
Old July 26th, 2017, 07:57 AM   #14
Dirtleg
Member
United States

Dirtleg is offline
 
Join Date: Dec 2014
Location: Virginia
Posts: 17
Ken, yes your FLL and Copy is definitely the more eloquent solution. Thank you for sharing it as I could see using it in the future.

In this instance as my customers maintenance department will ultimately inherit this I try not to use instructions they are most likely not familiar with. Some are much stronger in the PLC world than others.
Sad but unfortunately relevant.

And since the input for the path change was coming from an HMI I just used the last 3 digits of each IP as the Control List State value in the HMI and moved them into the path. That way it was a simple 1 rung of logic with a couple branches.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC504 pulling data from Controllogix using 1747-AENTR? Dariusincj LIVE PLC Questions And Answers 3 May 1st, 2017 11:21 PM
[Logix5000] ControlLogix PLC slamming wireless etherness radio with data defcon.klaxon LIVE PLC Questions And Answers 9 April 23rd, 2016 02:19 AM
ControlLogix Max REAL Data Size for MSG narcilla LIVE PLC Questions And Answers 5 July 25th, 2014 08:05 PM
MSG Command Leeroy LIVE PLC Questions And Answers 7 June 11th, 2013 10:21 PM
"CIP Data Read" MSG Help... JoseM LIVE PLC Questions And Answers 12 June 21st, 2012 08:54 PM


All times are GMT -5. The time now is 05:01 AM.


.