OkiePC
Sorry, it's been a while since I got back on. I ended up opening the recipe file on the SD card with the FactoryTalk file viewer and found there were two recipes referencing 4 tags. I made a UDT in the CompactLogix so that everything is internal in the PLC.
That sounds like a good modification.
On a different note, does anyone know if you can do a remote write to the G3 Kadet like you can to the PanelView for display navigation?
Yes, but you will have to put together the pieces.
You can create a numeric (integer) tag for remote control of the displayed page and then use a trigger on that tag to call a Program which decides which page to go to based on its value. On the Triggers tab choose "change in value" as the trigger type and put "1" as the value so that the action will be called each time the value changes.
In the program you can use the switch/case statement to run a GotoPage command for each value.
If you want a different tag in the PLC to tell it which page is being displayed, you can use the Page Properties > Actions > On Select field to write a value to that tag.
Also, don't name your program "GotoPage". Weird errors may occur when you try to translate the code if you use a reserved keyword as the name of the program.