Weird issue_Micrologix,HMI

rejoe.koshy

Member
Join Date
Dec 2011
Location
kolkata
Posts
195
Hi guys,
I have a PU dispensing machine installed at my end having MLX 1200 and 22711-TD HMI.The machine was running fine and suddenly the message starts showing up on the HMI screen, which says the "RTC module is missing, machine locked" & the outputs have been switched off.

The program is OEM locked & hence I cant view or upload the program .The OEM has sent me memory module & a memory card, with which I reloaded the PLC & HMI program but unfortunately , the machine is
still displaying the error.

There is no fault (hardware) on the PLC .I am in a fix trying to understand the reason such a problem.The hardware is all fine, there is no RTC module in PLC ,I have replaced the battery of the HMI unit...but issue still stands!!!

What could possibly go wrong??Is it possible that some remnants of the last program is retained by the PLC , even after reloading the program?
 
Last edited:
i am wondering if the HMI has a flat battery to keep the RTC internally! it may be in the PLC code that if that is not correct the unit alarms.


do you have a local Rockwell (Allen Bradley) sales rep you can ask for info.


http://literature.rockwellautomation.com/idc/groups/literature/documents/td/2711-td007_-en-p.pdf

Exactly!....I was thinking of the same & hence replaced the battery.The voltage read 2.95V (its a 3V battery) but didnt take a chance though and replaced it with a 3 V battery.
 
Exactly!....I was thinking of the same & hence replaced the battery.The voltage read 2.95V (its a 3V battery) but didnt take a chance though and replaced it with a 3 V battery.

If you measured the battery not connected to the hmi it may show ok once a load is applied you will find it can be much lower.

Let me know how you went.
 

Similar Topics

I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
Replies
8
Views
727
Hello all, I Have a PointIO module with 2 input cards. The Revision is 6.013 and it is connected to a ControlLogix running version 24.11 The...
Replies
16
Views
2,352
Hello all, I have a weird problem in rslogix 5000. Few of rungs the instruction shows UNK. I have the attached the screenshot of the program. I...
Replies
15
Views
8,066
We've been using a Digi One IAP as a Realport device (Serail to Ethernet) to allow a device (Dyadic actuator & amplifier -...
Replies
1
Views
2,918
Hi guys, Can I firstly say that, apart from today that I havent had much to do with Allen Bradley software/hardware, and when I do it always...
Replies
3
Views
3,855
Back
Top Bottom