PLC Analog Input signal Bouncing

Hello
I have a analog input signal that is bouncing
a bit. The PLC card is a 1769-IF8

I changed the input card filter setting
from 60hz to 50hz & the bouncing has greatly
decreased.

My question is does this affect the input card scaling
or accuracy by changing this filter setting?

Thanks
  Reply With Quote
Old April 6th, 2021, 08:33 AM   #2
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 3,175
Not on any brand/model that I’ve worked with.
  Reply With Quote
Old April 6th, 2021, 08:56 AM   #3
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,437
Some brands are ridiculous, I have not worked with a 1769-IF8 but have installed a 50ish 1769-IF4XOF2 and they are not bad, you can build your own filter but by doing so there is a little lag, most of the filters I have built are just time based so just slows down the update with some sort of scaling
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old April 6th, 2021, 02:10 PM   #4
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 3,063
i have had this issue before.

is the analog cable shielded and the drain wire grounded at the analog input card only?
check ALL wire terminations, from the source terminals to the input card itself.
check the terminals themselves, we had a bad terminal (broke inside the terminal) and had to replace it.
try to put a dummy signal at the device terminals and see f the input jumps around, the device may be bad or have bad terminations in the device.
james
  Reply With Quote
Old April 6th, 2021, 09:17 PM   #5
Ones_Zeros
Member
United States

Ones_Zeros is offline
 
Join Date: Feb 2014
Location: at work
Posts: 312
Thanks for the guidance
I appreciate it

I will definitely check all the terminations & cable shields.

Thanks
  Reply With Quote
Old April 7th, 2021, 08:55 AM   #6
mylespetro
Supporting Member
Canada

mylespetro is online now
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 331
How much bouncing are you talking about? Depends on the scaling and resolution, but if it's scaled 0-100% and it's bouncing from 20-30% that's not great, but if it's scaled 0-5 and it's bouncing from 1.28494-1.31843 I would consider that acceptable.
  Reply With Quote
Old April 7th, 2021, 06:03 PM   #7
Ones_Zeros
Member
United States

Ones_Zeros is offline
 
Join Date: Feb 2014
Location: at work
Posts: 312
I notice the bouncing when the process is down and no
Water is flowing through the flow meter.

Since this data has to be reported and when the process
is down the flow meter should read zero. It’s bouncing up to a positive number
and logging flow data when it shouldn’t.

I changed the filter setting on this particular analog input to
50hz and reduced the bouncing.

I appreciate all the help
Thanks
  Reply With Quote
Old April 7th, 2021, 06:17 PM   #8
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 3,063
when you say it bonces, just how much?
just because the process is down does not mean that a water valve may not open and allow water flow, that's why i asked how much.
it may be a small valve supplying coolant water, filling a process tank, or just to allow the water to flow and prevent materials from settling to the bottom of pipe(s). i have seen this occur at several plants.
james
  Reply With Quote
Old April 7th, 2021, 06:23 PM   #9
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: Montgomery, AL
Posts: 613
My advice isn't the solution you need, but for future readers, Keyence makes a flow meter that you can attach directly outside the pipe, and will measure the flow (not the most accurate), but if you just need to see it above a certain GPM and get an input back, it works great, but definitely $$$. Keyence may have a way to get you an analog reading back, but I'm unsure about it. It may be over EIP, so it's not analog, but integer/decimal format into PLC. But you probably using SLC, so may be worth more trouble than you looking for.
  Reply With Quote
Old April 7th, 2021, 07:01 PM   #10
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 5,266
Quote:
Originally Posted by Ones_Zeros View Post
I notice the bouncing when the process is down and no
Water is flowing through the flow meter.

Since this data has to be reported and when the process
is down the flow meter should read zero. It’s bouncing up to a positive number
and logging flow data when it shouldn’t.

I changed the filter setting on this particular analog input to
50hz and reduced the bouncing.

I appreciate all the help
Thanks
I am curious as to why changing the notch filter to 50Hz improved the noise rejection ?

Don't you guys over the pond use 60Hz mains frequency anymore ?

In class I always told my delegates to set the notch filter frequency to 50Hz for the UK, "for best immunity to noise generated by the mains wiring".

Anyway, don't rule out that the signal may be coming from the flow-meter itself, so you could test for this by substituting the flow-meter with a 4-20mA current source and running the process. If you still get bouncing you'll know it's wiring/cabling issues. If you don't, refer back to the flow-meter manufacturer.

EDIT : Are you confident that the flow-meter is installed correctly, to the manufacturers specifications ?

Most flow-meters I have used prefer to be in upwards vertical flow, and greater than a minimum distance, related to the pipe diameter, from a preceding bend.

Is there any entrained air or gas in the fluid ?

Have you actually proved there is no flow when the process is idle ?
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
Everything works with smoke. Let it out, and it stops working.

Nil Carborundem Illegitimi




Last edited by daba; April 7th, 2021 at 07:19 PM.
  Reply With Quote
Old April 8th, 2021, 10:20 AM   #11
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,929
Quote:
Originally Posted by Ones_Zeros View Post
I notice the bouncing when the process is down and no
Water is flowing through the flow meter.

Since this data has to be reported and when the process
is down the flow meter should read zero. It’s bouncing up to a positive number
and logging flow data when it shouldn’t.

I changed the filter setting on this particular analog input to
50hz and reduced the bouncing.

I appreciate all the help
Thanks
What are the details of the flow meter? Most magmeters have a setting to adjust how they cope with zero or low flow and some have settings that can be fine tuned for when there is air in the pipe (empty pipe threshold). Most electronic meters also have output filtering for their analog signals.

If it is just a simple prop meter with no programmability, I would be inclined to put a filter in the PLC code where you can trend and adjust the filter to optimize it.
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice.
  Reply With Quote
Old April 8th, 2021, 11:22 AM   #12
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,465
It's very common for any type of flow meter to have a "low flow cutoff". This can be a feature configurable in the flow meter itself or you can program it in your PLC.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old April 12th, 2021, 10:53 AM   #13
BClark4
Member
United States

BClark4 is offline
 
BClark4's Avatar
 
Join Date: Apr 2021
Location: South Carolina
Posts: 6
When there is "no flow" is there water stagnant inside the pipe or is it dry during the now flow condition. In the past I have noticed that slight vibrations can cause stagnant liquid to register a small flow. Also if you have any AC power 120V+ (wires for a pump perhaps) run adjacent to the signal wire the expanding and collapsing magnetic fields from these wires can induce voltage in your signal wire and create noise. if this is the case you can invest in shielding for your cable or perhaps enquire from the manufacturer about a filter to reduce this noise.

Also, What sort of cable is being used to connect the device with the plc?
  Reply With Quote
Old April 12th, 2021, 11:36 AM   #14
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: Barranquilla, Colombia
Posts: 3,006
I also noticed that if the flowmeter is pressurized, even with no flow the values will change slightly.
__________________
My two cents.
  Reply With Quote
Old April 12th, 2021, 11:42 AM   #15
CAD Services LLC
Lifetime Supporting Member
United States

CAD Services LLC is offline
 
Join Date: Mar 2021
Location: Spartanburg SC
Posts: 5
I would build a averaging logic

Quote:
Originally Posted by Ones_Zeros View Post
I notice the bouncing when the process is down and no
Water is flowing through the flow meter.

Since this data has to be reported and when the process
is down the flow meter should read zero. It’s bouncing up to a positive number
and logging flow data when it shouldn’t.

I changed the filter setting on this particular analog input to
50hz and reduced the bouncing.

I appreciate all the help
Thanks
If your main problem is that it is Recording a sec or two of data and you don't need to have a fast response then I would build a averaging logic.
Make a Clock one shot that you can change how fast it is, then use that to store about 5 to 10 samples, then average those to give you a just the value that is Turning On the Record request.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PWM to ANALOG Signal Conditioning ?? milmat1 LIVE PLC Questions And Answers 5 June 13th, 2016 08:46 AM
Analog input - Mitsubishi FX3G PLC / GX Developer joemev LIVE PLC Questions And Answers 7 March 25th, 2015 12:55 PM
Input on without giving plc a signal Linwo5 LIVE PLC Questions And Answers 10 March 4th, 2015 10:48 AM
redundant analogue input Amr Hassan LIVE PLC Questions And Answers 10 July 27th, 2005 09:56 AM
Connecting self-powered analog signal to Moore PLC shyampv LIVE PLC Questions And Answers 2 May 13th, 2002 10:49 AM


All times are GMT -4. The time now is 12:20 PM.


.