Hello everyone,
For my new project I want to integrate a Staübli Robot with AB PLC. I don't know how to get started with it. How can I integrate the Robot in Studio 5000 Logix Designer via Ethernet I/P. I look forward to your expert suggestions |
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2015
Location: Yokohama
Posts: 545
|
You have to add the EDS (electronic data sheet) for the robot provided by Staüblito the Logix Studio EDS catalogue. Then you can add this hardware to the EtherNet/IP IO for this Logix processor, configure the IP address of the robot, the required connection(s) and RPI (request packet interval) just like any other EtherNet/IP adapter device. Once you configure the robot the Logix Studio will generate the "tags" for the connections of the robot, which is the name for the variables within the Logix program for the inputs, outputs and status information of the robot. The PLC Logic is developed by referring to these tags. I suggest if you are new to EtherNet/IP and Rockwell technology, that you have a look at the Rockwell literature.
|
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Oct 2020
Location: Germany
Posts: 13
|
Thank you so much for the reply.
![]() |
![]() |
![]() |
#4 |
Member
|
From this catalog: https://www.staubli.com/en/file/7985.show
Unless you have the CS9/CS9MP, seems like you would also have to purchase the particular option for Ethernet I/P. Apart from that, what Alfred said ![]() -PreLC
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC. ![]() Last edited by PreLC; April 8th, 2021 at 09:33 AM. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
TCP/IP Communication between CompactLogix PLC/ Matlab | AnotherPLCguy | LIVE PLC Questions And Answers | 2 | May 2nd, 2019 11:55 PM |
CompactLogix L32E PLC need to change its IP | DavidRuan | LIVE PLC Questions And Answers | 6 | September 6th, 2016 07:52 PM |
Reading selected language on PanelView by CompactLogix PLC | amberman | LIVE PLC Questions And Answers | 2 | December 4th, 2014 09:31 AM |
Rs logix 5000 | varunmahendran91 | LIVE PLC Questions And Answers | 4 | October 6th, 2014 02:26 PM |
MPI comunication | Manuel Raposo | LIVE PLC Questions And Answers | 22 | July 16th, 2007 07:24 AM |