Earth MSG Read SLC -> 5069 L320

Hello. I have a new 5069 L320ER that I installed and I am trying to read and write data to an existing SLC5/05 via Ethernet.

They are both on the same network. I am attempting to use port A1 on the Compactlogix. I set the type as SLC typed Read, and the address as 3, xxx.xxx.xxx.xxx where xxx is the ip to the SLC5/05.. It goes to connection failed immediately. What am I missing?

Thank you in advance!
  Reply With Quote
Old April 4th, 2021, 01:25 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,819
Is the SLC-5/05 more than about 20 years old ?

Early revisions didn't support the CIP protocol that ControlLogix does.

One quick way to find out is to use the EtherNet/IP driver in RSLinx Classic instead of the older Ethernet Devices driver. If the SLC shows up, then it's new enough to support CIP.
  Reply With Quote
Old April 4th, 2021, 03:35 AM   #3
twilliams
Member
United States

twilliams is offline
 
Join Date: Apr 2020
Location: Las Vegas
Posts: 4
Quote:
Originally Posted by Ken Roach View Post
Is the SLC-5/05 more than about 20 years old ?

Early revisions didn't support the CIP protocol that ControlLogix does.

One quick way to find out is to use the EtherNet/IP driver in RSLinx Classic instead of the older Ethernet Devices driver. If the SLC shows up, then it's new enough to support CIP.
After a bit of trying, I can't seem to get anything on EtherNet/IP in RSLinx. It does not seem to like to cross subnets.

I have it working with another SLC5/05, and some PLC 5s but for whatever reason I cannot directly communicate between these two. I was able to read the SLC5/05 with an old PLC5 40E, then read the PLC5 from the new Contrologix. I don't understand why I cannot talk directly to the SLC.

Even when reading the SLC from the PLC5, I had to use a PLC5 typed read.
  Reply With Quote
Old April 7th, 2021, 01:14 PM   #4
twilliams
Member
United States

twilliams is offline
 
Join Date: Apr 2020
Location: Las Vegas
Posts: 4
Thank you for your help. After diving in further and trying many things including messaging to and from other SLC5/05s and trying from another ControlLogx, it appears this is an old SLC that cannot communicate via modern CIP message standards.

I was able to work around this issue using a temp fix by message read and write from a PLC5 40E, and then to my new CompactLogix.
  Reply With Quote
Old April 7th, 2021, 03:33 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,819
Thanks for the update !

I slacked off a little on you by only describing the RSLinx driver method for figuring out the communications ability of an old SLC-5/05.

Because I'm familiar with the controllers, I would have looked at the Device Properties in RSLinx and looked for an "Firmware Revision Number" of FRN5 or higher. Similar information can be seen in the embedded Web pages for the controllers and in the Controller section of RSLogix 500.

The other confirming method is to test the controller's ability to open a TCP socket on a specific port. I use TCPing because I've been using it for ages and it always gives me the correct result. 20-year-old SLC-5/05's without CIP support only open a TCP connection on Port 2222, while "modern" SLCs will open a connection on both 2222 and 44818.

Code:
tcping [ip address] 2222       Legacy A-B Client-Server protocol
tcping [ip address] 44818      CIP protocol over EtherNet/IP
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
adding slc 500 to rs5000 for messaging Rippey574 LIVE PLC Questions And Answers 15 September 12th, 2017 06:24 AM
MLX1400 MSG Read from CLX Is Very Slow scarince LIVE PLC Questions And Answers 0 August 29th, 2017 08:02 AM
PLC5 MSG Instruction to read from SLC 5 Carmelo LIVE PLC Questions And Answers 1 March 9th, 2015 03:23 PM
Micrologix 1500 LRP MSG READ from Compactlogix asmaint2 LIVE PLC Questions And Answers 2 April 9th, 2012 12:18 PM
AB SLC 5/05 Ethernet MSG Errors mrdegold LIVE PLC Questions And Answers 7 January 20th, 2009 01:10 PM


All times are GMT -4. The time now is 01:58 PM.


.