i did some changes to the program and its working just fine, as it supposed to according to the exercise, is there anything wrong where you can help me to improve it?
Attached Images
File Type: jpg LadderRungs2.jpg (75.1 KB, 11 views)
  Reply With Quote
Old April 6th, 2021, 09:20 PM   #17
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,602
Quote:
Originally Posted by Aintbad View Post
i did some changes to the program and its working just fine, as it supposed to according to the exercise, is there anything wrong where you can help me to improve it?



Well done!


I would do the flip-flop (rung 005) a little differently, but that's just a style issue. You might want to ask The Google about [ladder logic flip-flop] and see if there are any arrangements that are more clear. I'm partial to the top two rungs of the image below.


Does LogixPro allow for comments?




You can get rid of Rungs 001 and 002, and also intermediate bits B3:0/2 and B3:0/4 by
  1. Putting O:0/2 at the start of rungs 003 and 004,
  2. Replacing the two [XIC B3:0/2] instructions with [XIO I:1/2],
  3. Replacing the two [XIC B3:0/4] instructions with [XIO I:1/3].
That would not change the behavior, but I think it will be a bit more clear; that said, the inverted logic on the inputs might be confusing, so maybe change the names of I:1/2 and I:1/3 to something like [0 for low pressure, one motor one] and [0 for low low pressure, both motors on], respectively.



Last edited by drbitboy; April 6th, 2021 at 09:26 PM.
  Reply With Quote
Old April 6th, 2021, 09:48 PM   #18
Aintbad
Member
Canada

Aintbad is offline
 
Join Date: Apr 2021
Location: London
Posts: 9
Quote:
Originally Posted by drbitboy View Post
Well done!


I would do the flip-flop (rung 005) a little differently, but that's just a style issue. You might want to ask The Google about [ladder logic flip-flop] and see if there are any arrangements that are more clear. I'm partial to the top two rungs of the image below.


Does LogixPro allow for comments?




You can get rid of Rungs 001 and 002, and also intermediate bits B3:0/2 and B3:0/4 by
  1. Putting O:0/2 at the start of rungs 003 and 004,
  2. Replacing the two [XIC B3:0/2] instructions with [XIO I:1/2],
  3. Replacing the two [XIC B3:0/4] instructions with [XIO I:1/3].
That would not change the behavior, but I think it will be a bit more clear; that said, the inverted logic on the inputs might be confusing, so maybe change the names of I:1/2 and I:1/3 to something like [0 for low pressure, one motor one] and [0 for low low pressure, both motors on], respectively.


oh okay! thank you and yes you can add comments in every rung!
ill start the Part 4 and see how it goes...
ill post again if i have any more questions...
Thanks again.
  Reply With Quote
Old April 7th, 2021, 07:04 AM   #19
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,602
I thought of one more thing: a few posts ago you showed PE2 (I:1/3) parameters of high limit = 118 and span = 20. So I:1/3 will become 1 when the pressure is above 118; I:1/3 will become 0 when the pressure is below 98 (=118-20); I:1/3 will not change otherwise.


With the current logic, if the load is such that two compressors are required (as determined by the pressure continuing to drop to 98 after one compressor starts running at 100), then that PE2 high limit of 118 means the second compressor will turn off when I:1/3 becomes 1, which will happen before the system pressure rises to 120. Assuming the load is still high, the remaining compressor will not be able to get the system to 120. In that case, as long as the load stays high, I:1/2 will never become 1, and the same compressor will always come on first.
  Reply With Quote
Old April 7th, 2021, 03:31 PM   #20
Aintbad
Member
Canada

Aintbad is offline
 
Join Date: Apr 2021
Location: London
Posts: 9
Quote:
Originally Posted by drbitboy View Post
I thought of one more thing: a few posts ago you showed PE2 (I:1/3) parameters of high limit = 118 and span = 20. So I:1/3 will become 1 when the pressure is above 118; I:1/3 will become 0 when the pressure is below 98 (=118-20); I:1/3 will not change otherwise.


With the current logic, if the load is such that two compressors are required (as determined by the pressure continuing to drop to 98 after one compressor starts running at 100), then that PE2 high limit of 118 means the second compressor will turn off when I:1/3 becomes 1, which will happen before the system pressure rises to 120. Assuming the load is still high, the remaining compressor will not be able to get the system to 120. In that case, as long as the load stays high, I:1/2 will never become 1, and the same compressor will always come on first.

Yes you're right, that was my bad.
i was playing with the values to test it and for some reason when i took the screenshot it was set like that but in my assignment the values i got to use are 120 / 10 for the first motor and 120 11 for the second one.
  Reply With Quote
Old April 7th, 2021, 05:29 PM   #21
PLCnovice61
Member
Australia

PLCnovice61 is offline
 
Join Date: Apr 2015
Location: home
Posts: 317
aintbad, in the download section under AB, is the dual compressor ex#4, done by the master of logixpro 10,000 poster Lance1, you wont get a better example of how to do things in programming than by Lancie1.
But of course you need to try and do the exercises without any help, that is how you learn. Keep trying/thinking about what should/shouldn't happen then trial it in code. LogixPro is a fantastic learning/training tool, but be aware it isn't 100% exactly how a AB processor works
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
logixpro 500 dual compressor simulator herb61 LIVE PLC Questions And Answers 3 July 17th, 2017 03:41 PM
Dual Compressor Logixpro Help please vietkidx LIVE PLC Questions And Answers 2 March 22nd, 2014 12:17 PM
Dual Compressor PLEASE HELP DUE VERY SOON! vietkidx LIVE PLC Questions And Answers 13 March 3rd, 2014 07:47 PM
Logixpro dual Compressor mwortman LIVE PLC Questions And Answers 3 November 30th, 2012 05:28 PM
Revisiting Dual Compressor Simulation for Logixpro brennan84 LIVE PLC Questions And Answers 0 April 30th, 2010 04:10 PM


All times are GMT -4. The time now is 01:23 PM.


.