Smile Panelview Plus7, Factorytalk

Is there a way to find out which MER your panelview is running on startup whenever you have multiple files in the internal storage? Instead of having to walk up to it and go into the settings on the terminal.
  Reply With Quote
Old April 7th, 2021, 04:51 PM   #2
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 5,266
I don't think there is.

Even if the running MER is exposed as a System tag, I don't think there is a way to interrogate it externally.

If you, and only you, have access to transfer files to the PV, then there might be an entry in the FactoryTalk logs, and in might say what the transfer parameters (i.e. Set Run at Startup) were at the time of download.

I can't check on anything View Studio at the moment, my installation doesn't start-up,, giving a cryptic error. I will have to uninstall and re-install FTVStudio I think, but I'm loathe to do that just right now as it might mess up all my installations of RSLogix/Studio5000. I can't afford the 2 days plus to re-install all of that lot !!
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
Everything works with smoke. Let it out, and it stops working.

Nil Carborundem Illegitimi



  Reply With Quote
Old April 7th, 2021, 06:20 PM   #3
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 3,063
May i suggest that you add a screen with the details on it in regards to the information you need that is accessible.
james
  Reply With Quote
Old April 7th, 2021, 06:33 PM   #4
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 5,266
Quote:
Originally Posted by James Mcquade View Post
May i suggest that you add a screen with the details on it in regards to the information you need that is accessible.
james
To me it was obvious James, he doesn't want to go to the PView, but wants to know what MER it is running.

I don't even know if it is a system variable that could be displayed on a screen, but if he has to go to the PView to see it, he could easily go through the config screens to find it.

My guess is he wants to remotely access it.

I'm thinking that Asset Manager might be able to see it, just don't know the details ....

Just had the thought that RSLinx might show it ....
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
Everything works with smoke. Let it out, and it stops working.

Nil Carborundem Illegitimi



  Reply With Quote
Old April 12th, 2021, 07:07 PM   #5
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,274
I had to solve this exact problem a couple of months back. Multiple .mer files on a PVP7, no clear indication of which one was running. OEM did not provide a password to allow me to enter configuration mode to see which one was loaded, and all of my usual get-to-config-mode tricks like pressing the white square a bootup, or Ctrl+Alt+Shift+Windows failed me.

In the end I solved it like this:
1. Upload all .mer files using ME Transfer Utility
2. Restore first .mer file into FTView Studio and make a small visual edit
3. Create runtime from the edited file
4. Download to to HMI using ME Transfer Utility using the exact same filename BUT VERY IMPORTANT deselect the "run application at startup" checkbox first
5. Reboot the HMI

What this does is updates that .mer file on the HMI but does not change which file is run at startup. So, when the HMI boots up, if it contains the graphical edit you made, then the file you edited is the "live" one, the one that is being run by the HMI. If it doesn't, you can eliminate that .mer file as a possiblity and repeat steps 2 through 5 until you find it.

Once you're done, make sure to download all of the original .mer files back to the PVP so that it's left in the same state you found it.

Or, you know, delete the redundant files from your god dang HMI's so that I don't waste half a day cleaning up behind you
  Reply With Quote
Old April 12th, 2021, 07:23 PM   #6
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 5,266
Quote:
Originally Posted by ASF View Post
I had to solve this exact problem a couple of months back. Multiple .mer files on a PVP7, no clear indication of which one was running. OEM did not provide a password to allow me to enter configuration mode to see which one was loaded, and all of my usual get-to-config-mode tricks like pressing the white square a bootup, or Ctrl+Alt+Shift+Windows failed me.

In the end I solved it like this:
1. Upload all .mer files using ME Transfer Utility
2. Restore first .mer file into FTView Studio and make a small visual edit
3. Create runtime from the edited file
4. Download to to HMI using ME Transfer Utility using the exact same filename BUT VERY IMPORTANT deselect the "run application at startup" checkbox first
5. Reboot the HMI

What this does is updates that .mer file on the HMI but does not change which file is run at startup. So, when the HMI boots up, if it contains the graphical edit you made, then the file you edited is the "live" one, the one that is being run by the HMI. If it doesn't, you can eliminate that .mer file as a possiblity and repeat steps 2 through 5 until you find it.

Once you're done, make sure to download all of the original .mer files back to the PVP so that it's left in the same state you found it.

Or, you know, delete the redundant files from your god dang HMI's so that I don't waste half a day cleaning up behind you
Brilliant !

Wish there was Like and Love buttons like on facebook, but we have to make a post ...
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
Everything works with smoke. Let it out, and it stops working.

Nil Carborundem Illegitimi



  Reply With Quote
Old April 16th, 2021, 04:42 AM   #7
JonasVC
Member
Belgium

JonasVC is offline
 
Join Date: Sep 2020
Location: Antwerp
Posts: 1
Quick suggestion: always add dates on the name of your files
example: Line1_20210416
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
FactoryTalk View ME Runtime/Run after download to Panelview Plus Baker in Virginia LIVE PLC Questions And Answers 4 November 28th, 2019 03:56 PM
Problem using faceplate for panelview HMI in factorytalk studio. plc_student77 LIVE PLC Questions And Answers 1 July 22nd, 2016 03:50 PM
RSLogix 5000 ver. 23 & FTView 8.0 jkerekes LIVE PLC Questions And Answers 16 February 12th, 2015 02:02 AM
FactoryTalk HMI architecture computers and panelview mix V0N_hydro LIVE PLC Questions And Answers 2 January 7th, 2014 11:45 AM
RS Linx Classic Read Only ronman LIVE PLC Questions And Answers 26 October 11th, 2013 10:44 AM


All times are GMT -4. The time now is 01:21 PM.


.