Hello forum members,

A colleague of mine is developing a SCADA system for one of my projects with Wonderware InTouch speaking to a Siemens S7 PLC by Ethernet.

1). Is it possible to set the limit value of one tag with the value of another tag? I find this feature really useful in WinCCFlexible.

2.) Does Intouch have such a thing as a Textlist where by a different text string can be displayed based on the value of an integer tag? If so, can the texts be linked to tags?

3). Is it possible to indirectly address tags? E.G. DB[Variable1].DBW[Variable2]

The last one, in particular, I think is a long shot.

Nick
 
1, Yes.
2, No, but you can do it with some concat string expressions, and its commonly done.
3. Yes, but its more involved than that.
 
What is your Wonderware configuration and revisions?
Because, the answer could be yes to all dependent on your configuration and revision.
 
Oakley,

Thanks for your reply, this will be a stand alone system with Intouch V10.1

Earthscape,

Thanks for your reply, would you care to elucidate?

Nick
 

Similar Topics

Hello, I recently updated my controls system from standalone Intouch to Wonderware System Platform 2014 and Intouch 2014, using Achestra IDE...
Replies
2
Views
4,562
Hola chicos. Tengo un problema con el driver de comucicacion dasabcip 5, y un plc controllogix v34, ya realice la comunicacion pero en ciertos...
Replies
2
Views
102
Hi, I am upgrading a Wonderware SCADA form version 9.5 to version 23. I am able to migrate all the graphic, but when to activate the runtime this...
Replies
8
Views
334
Hi all, I am using OI.GATEWAY.2 to communicate to the PLC using an OPC UA. I can see the tags using an OPC explorer connecting to the...
Replies
0
Views
129
For a while, I have been working with InTouch 10.1. The problem I am currently facing is the need to implement certain functions that do not...
Replies
0
Views
440
Back
Top Bottom