Red lion G306A000 - fuji electric pxr4 temp regilator

Good day !

I hope someone is willing to give me advise....

I'm new to programming over RS485

I have a G306A000 that i want to be able to communicate with 3 x pxr4(fuji electric) temp regilators over Rs485 ....

The problem is i have no idea where to start.
If anyone could explain or help me find some info i could use i would be really happy.

What i need to do is to be able to see the temp from the regilators on the hmi and set the setpoint from the HMI

Best Regards
Fannar
  Reply With Quote
Old October 11th, 2017, 11:39 AM   #2
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,024
http://accautomation.ca/click-plc-se...-instructions/

The above thread will show a Click PLC communicating RS485 to a Solo Process Temperature controller. The communication protocol is Modbus RTU. The PLC is the Master and the Temperature controller is the Slave.
The process of connecting the HMI to the Temperature controllers is similar.
Hope this helps you out.
Regards,
__________________
Garry
http://www.accautomation.ca
  Reply With Quote
Old October 12th, 2017, 10:37 AM   #3
fannar
Member
Iceland

fannar is offline
 
Join Date: Oct 2017
Location: iceland
Posts: 7
Dear
Garry

Thanks for the helpful info.

I can see in this example that the modbus dataregister for the Solo regliator is "44097" for Process Value (PV).

I cant find the manual for fuji electric pxr4 regilator to find the dataregisters.

Please correct me if thats not where to look for the data registers.

regards
Fannar
  Reply With Quote
Old October 12th, 2017, 12:07 PM   #4
mhammer214
Member
United States

mhammer214 is offline
 
Join Date: Jul 2013
Location: Colorado
Posts: 19
This link has the manual for Modbus control of the PXR temperature controllers including a Modbus address map:
http://www.skylarkcontrols.com/pdf_f...S_Protocol.pdf
Hope this helps
  Reply With Quote
Old October 12th, 2017, 07:00 PM   #5
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,024
https://americas.fujielectric.com/fi...2642d-E%29.pdf

Hi Fannar,
You are correct in looking for the modbus addresses. The above link will take you to the manual where you will find examples of the addresses to use.
I did a google search for "Fugi PXR4 Modbus Addresses" to find the link.

Regards,
__________________
Garry
http://www.accautomation.ca
  Reply With Quote
Old October 13th, 2017, 05:46 AM   #6
fannar
Member
Iceland

fannar is offline
 
Join Date: Oct 2017
Location: iceland
Posts: 7
Thanks guys for all your help!

I have two other questions.

Can someone explain Parity ? and how to set it ?

and does someone know what wires i have to connect to the rj45 plug for redlion they are market TxB , TxA , Rxa , RxB and so one. But i need to find out witch one is the + and witch one is the - for two wire connection.

Best regards
Fannar
  Reply With Quote
Old October 13th, 2017, 06:07 AM   #7
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,024
"Parity is a method of detecting errors in transmission. When parity is used with a serial port, an extra data bit is sent with each data character, arranged so that the number of 1 bits in each character, including the parity bit, is always odd or always even. If a byte is received with the wrong number of 1s, then it must have been corrupted. However, an even number of errors can pass the parity check."

In the PXR4 it is in section 4.1 Set Items of the above manual.
Set them by operating the front panel keys.
CoM Parity setting 0 (default)
0: odd parity
1: even parity
2: none parity

The following data sheet will show the RS485 pin connection.
http://www.redlion.net/sites/default...%20only%29.pdf

Regards,
__________________
Garry
http://www.accautomation.ca
  Reply With Quote
Old October 13th, 2017, 09:55 AM   #8
fannar
Member
Iceland

fannar is offline
 
Join Date: Oct 2017
Location: iceland
Posts: 7
Big thanks to all of you guys !

Everything works now with the regilator , i'am able to read data as well as writing set point to the regilator,

With red lion i have used a button that call Program1()

within program 1 i set the setpoint to 50°C
then i have if statement in the programme

programmed_setpoint := 50;
if(real_temperature >= programmed_setpoint){
GotoPage(Page2);
}

i wated for the temp to reach 50 but nothing happend .... does the program only run after the button is pressed ? is there no way to have the if statement waiting for the temp to reach the setpoint ?

Regards
Fannar
  Reply With Quote
Old Yesterday, 04:02 AM   #9
fannar
Member
Iceland

fannar is offline
 
Join Date: Oct 2017
Location: iceland
Posts: 7
Anyone has the answer ?
  Reply With Quote
Old Yesterday, 06:02 AM   #10
BenDruck
Member
United States

BenDruck is offline
 
Join Date: Oct 2015
Location: US
Posts: 6
Quote:
Originally Posted by fannar View Post
Anyone has the answer ?
You’re doing way more work than you need to. Simply select the real_temperature tag, click on the “Triggers” tab.
Set “Trigger Mode” = Ablolute High
Set “Value” = 50
Set “Action” = GotoPage(Page2)
  Reply With Quote
Old Yesterday, 06:28 AM   #11
fannar
Member
Iceland

fannar is offline
 
Join Date: Oct 2017
Location: iceland
Posts: 7
Hey

Thanks for your answer,
the problem is i have 3 different temperatures that have to reach temp before going to page3.

Regarsd
Fannar
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Red Lion Data Station Plus Question Jmoreno111 LIVE PLC Questions And Answers 1 April 6th, 2015 10:55 PM
Red Lion to Emerson EN BlueAltezza LIVE PLC Questions And Answers 2 February 25th, 2015 07:46 AM
Red Lion G15 HMI for Temp control no PID John McCoy LIVE PLC Questions And Answers 12 March 17th, 2014 02:24 PM
Red Lion Cognex comms Problem, writing value to wrong Tags wdd0422 LIVE PLC Questions And Answers 5 October 29th, 2013 11:43 AM
Red Lion G3 to Watlow F4 temp controller jeffj44646 LIVE PLC Questions And Answers 5 October 1st, 2010 03:07 PM


All times are GMT -5. The time now is 09:50 AM.


.