Old October 12th, 2017, 09:47 AM   #16
rootboy
Lifetime Supporting Member
United States

rootboy is offline
 
rootboy's Avatar
 
Join Date: Jan 2004
Location: Tennessee
Posts: 1,251
In rung 6 take out everything except the timer .DN bit. You've already got it doing the same thing for you in rung 4.

Rung 7 looks rather suspicious to me, is it your intent to only check to see if conveyor 1 has been started, and not actually running?
__________________
Just because you can doesn't mean that you should...
  Reply With Quote
Old October 12th, 2017, 11:53 AM   #17
backendcode
Member
Canada

backendcode is online now
 
Join Date: Aug 2017
Location: brampton
Posts: 156
Quote:
Originally Posted by Mispeld View Post
IMHO and experience, the original code is more mainstream with respect to starting and stopping conveyor motors.

That said, there seems to be redundancy with the timers and stop/start logic. For example, the stop bits may not need to be on both the timer and OTE instructions. I cannot say for sure without knowing whether the timer bits are used elsewhere in the program.

My advice would be to consider the purpose of the timer, and limit its precondition to just those aspects that you want to delay. For example, is it just sensor response time ("de-bounce"), or does it include startup/run time of a downstream conveyor? Then use that .DN bit, latched and unlatched as necessary, to energize the OTE. Again, in this example, the stop bit would unlatch the OTE, but not be part of the timer, unless the timer is used elsewhere.
Mispeld, These timers are just for sensor response time because this is inspection line and door will be moving on the conveyors, I want to avoid the situation where guy comes to conveyor and lift up the door for a sec to have a look so this timer will avoid that debounce time.

Thanks,
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 12th, 2017, 11:55 AM   #18
backendcode
Member
Canada

backendcode is online now
 
Join Date: Aug 2017
Location: brampton
Posts: 156
Quote:
Originally Posted by LoganB View Post
I can suggest a couple of things. You might want to add descriptions to some of those bits. For instance, "Line_2_Running_Bit", is this monitoring the MCR for the line? Or is it an Auto Mode flag? Try to make it so that people could understand exactly what each instruction is doing without seeing the machine the run.

The code itself isn't overly complex. If you clarify what everything is doing I think you'll be ok. Don't be afraid to document too much. Use rung comments and descriptions whenever you can.
yes line 2 running bit check the state of MCR and thank you for the advice, I am going to comment each rung and instructions so this will help someone in future.

Thank you again,
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 12th, 2017, 11:57 AM   #19
backendcode
Member
Canada

backendcode is online now
 
Join Date: Aug 2017
Location: brampton
Posts: 156
thanks everyone for comment and I am gong to stick with the same code but try to reduce the code and also I will put comments and description in my PLC code.

Thank you for the input!
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 12th, 2017, 12:00 PM   #20
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 2,955
Don't reduce the code if it means losing readability/understanding how the logic works.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old October 12th, 2017, 12:01 PM   #21
backendcode
Member
Canada

backendcode is online now
 
Join Date: Aug 2017
Location: brampton
Posts: 156
Quote:
Originally Posted by jstolaruk View Post
Don't reduce the code if it means losing readability/understanding how the logic works.
Ok, Make sense! I won't
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 12th, 2017, 12:16 PM   #22
gerberz
Member
United States

gerberz is offline
 
Join Date: Jan 2017
Location: no
Posts: 4
Having a hard time understanding what you want. You said you have 3 motors and 3 prox's. What is this part present for the conveyor? Is the prox the part present or are you trying to use a memory bit?
  Reply With Quote
Old October 15th, 2017, 10:20 AM   #23
Tark
Member
United States

Tark is offline
 
Tark's Avatar
 
Join Date: Apr 2004
Posts: 494
Let me start by saying congrats on completing you first program. I’m assuming this thread is about the conveyor you posted about in the My first PLC project finished! thread.

The way I would have tackled the program will take more lines of code than the 5 you are showing. Your code does take a part placed on the conveyor and moves it to the first open spot on the conveyor. But in watching the YouTube video you posted I see some problems. As you are eluding to in this post, the part movement is inefficient. With your code the part stops at each conveyor or what I would call a station before it moves to the next station even though there is no part at the next station. What I think you’re looking to accomplish is when the conveyor is empty and you place a part on it, the part should be moved to the front of the conveyor without stopping. There are some other issues as well, what happens if a motor fails to run (tripped overload), what happens if a part is taken off the conveyor, what happens if a motor is running but a part doesn’t move? What if the conveyor had 6 stations instead of the 3? If you start adding to your program to account for these what if’s, you might end up with a mess. The issue I see is that your program isn’t broken down into logical blocks, it lacks structure or architecture.

First, I would change your naming convention. The entire piece of equipment is the ‘conveyor’, so I wouldn’t have named the parts of the ‘conveyor’ (like the motors and sensors) conveyor[1], conveyor[2], conveyor[3]. This causes some confusion, does this program run more than one ‘conveyor’? Your comment for rung 4 denotes a better name for these parts of the ‘conveyor’, that being Section. Personally I would call these parts of the ‘conveyor’ Station1, Station2, Station3, but even Section1, Section2, and Section3 is better name than conveyor[1], conveyor[2], and conveyor[3], plus it’s easier to read. You might also consider using Camel Case when naming your symbols, some designers limit the amount of characters you can use for a name and using Camel Case will allow you to get rid of the dashes and still allow your names to be readable, i.e. Station1MotorControl. Also, don’t put the word ‘bit’ in your names (line_2_running_bit), we already know it’s a bit . When you name symbols, determine if the symbol is a command or status and name it accordingly. I’m thinking Line2Running is a command, so it should be called Line2Run. Your Motor_control would be called Run because it’s a command, a signal back from the motor would be called Running. You have a Start_sensor and Stop_sensor, but is that what they really are? Are they the InfeedSensor and OutfeedSensor? Your Start_timer, we already know it’s a timer, what’s its purpose? Would a better name be StartDelay or RunDelay?

Order of the logic. When I look at the five rungs you posted I see one thing common between all of them, that being line_2_running_bit. But where that bit is placed on each of the rungs it’s hard to see that it is common. If you place the line_2_running_bit bit (that sounds redundant now doesn’t it ) first in the five rungs it makes it easier to see why an entire section of code isn’t running. This will make it easier to troubleshoot.

For the logical blocks, the program structure, I would have done this. There is a Conveyor object and Station objects. The Conveyor object controls the state of the conveyor. It knows the push-button states, controls the indicators, e-stop logic is probably done there as well. It determines if the conveyor should run or not. The Conveyor object tells the Station objects to run. The Station objects tell the Conveyor object if they are in alarm. The Station objects convey information to one another, am I Ok, can I receive a part, am I sending a part. The code for Station 1, 2, and 3 is the same except for mapping of information between the stations, this gives you code reuse. How a station determines how they run their motor, whether there is a part present or not, doesn’t matter to the other stations. The other stations only care about, can I send you a part, are you Ok, and here comes a part. So the logic for Station1 shouldn’t have Station2’s senor or motor status in it, it should only have Station2’s StatusOk and InfeedAvailable status in it. Coding to logical blocks lets you focus on smaller pieces for the program instead of the entire program at once. Notice your original post is concerned with how to control all three motors. What you need to think about is how to control each individual motor. A Station is only concerned with the station before it and after it. So in actuality you only need to think about how to control and individual station. From there you organize your data into logical blocks of memory, so you might use one word for the status of the station and another word for the alarms of the station.
Attached Images
File Type: jpg Capture.jpg (31.2 KB, 55 views)
  Reply With Quote
Old Yesterday, 09:34 PM   #24
backendcode
Member
Canada

backendcode is online now
 
Join Date: Aug 2017
Location: brampton
Posts: 156
Quote:
Originally Posted by Tark View Post
Let me start by saying congrats on completing you first program. I’m assuming this thread is about the conveyor you posted about in the My first PLC project finished! thread.

The way I would have tackled the program will take more lines of code than the 5 you are showing. Your code does take a part placed on the conveyor and moves it to the first open spot on the conveyor. But in watching the YouTube video you posted I see some problems. As you are eluding to in this post, the part movement is inefficient. With your code the part stops at each conveyor or what I would call a station before it moves to the next station even though there is no part at the next station. What I think you’re looking to accomplish is when the conveyor is empty and you place a part on it, the part should be moved to the front of the conveyor without stopping. There are some other issues as well, what happens if a motor fails to run (tripped overload), what happens if a part is taken off the conveyor, what happens if a motor is running but a part doesn’t move? What if the conveyor had 6 stations instead of the 3? If you start adding to your program to account for these what if’s, you might end up with a mess. The issue I see is that your program isn’t broken down into logical blocks, it lacks structure or architecture.

First, I would change your naming convention. The entire piece of equipment is the ‘conveyor’, so I wouldn’t have named the parts of the ‘conveyor’ (like the motors and sensors) conveyor[1], conveyor[2], conveyor[3]. This causes some confusion, does this program run more than one ‘conveyor’? Your comment for rung 4 denotes a better name for these parts of the ‘conveyor’, that being Section. Personally I would call these parts of the ‘conveyor’ Station1, Station2, Station3, but even Section1, Section2, and Section3 is better name than conveyor[1], conveyor[2], and conveyor[3], plus it’s easier to read. You might also consider using Camel Case when naming your symbols, some designers limit the amount of characters you can use for a name and using Camel Case will allow you to get rid of the dashes and still allow your names to be readable, i.e. Station1MotorControl. Also, don’t put the word ‘bit’ in your names (line_2_running_bit), we already know it’s a bit . When you name symbols, determine if the symbol is a command or status and name it accordingly. I’m thinking Line2Running is a command, so it should be called Line2Run. Your Motor_control would be called Run because it’s a command, a signal back from the motor would be called Running. You have a Start_sensor and Stop_sensor, but is that what they really are? Are they the InfeedSensor and OutfeedSensor? Your Start_timer, we already know it’s a timer, what’s its purpose? Would a better name be StartDelay or RunDelay?

Order of the logic. When I look at the five rungs you posted I see one thing common between all of them, that being line_2_running_bit. But where that bit is placed on each of the rungs it’s hard to see that it is common. If you place the line_2_running_bit bit (that sounds redundant now doesn’t it ) first in the five rungs it makes it easier to see why an entire section of code isn’t running. This will make it easier to troubleshoot.

For the logical blocks, the program structure, I would have done this. There is a Conveyor object and Station objects. The Conveyor object controls the state of the conveyor. It knows the push-button states, controls the indicators, e-stop logic is probably done there as well. It determines if the conveyor should run or not. The Conveyor object tells the Station objects to run. The Station objects tell the Conveyor object if they are in alarm. The Station objects convey information to one another, am I Ok, can I receive a part, am I sending a part. The code for Station 1, 2, and 3 is the same except for mapping of information between the stations, this gives you code reuse. How a station determines how they run their motor, whether there is a part present or not, doesn’t matter to the other stations. The other stations only care about, can I send you a part, are you Ok, and here comes a part. So the logic for Station1 shouldn’t have Station2’s senor or motor status in it, it should only have Station2’s StatusOk and InfeedAvailable status in it. Coding to logical blocks lets you focus on smaller pieces for the program instead of the entire program at once. Notice your original post is concerned with how to control all three motors. What you need to think about is how to control each individual motor. A Station is only concerned with the station before it and after it. So in actuality you only need to think about how to control and individual station. From there you organize your data into logical blocks of memory, so you might use one word for the status of the station and another word for the alarms of the station.
Tark,
First of all, I would like to thank you for taking your time out and gave your feedback on my thread. I really appreciate that!

I didn't post the complete code in this thread but I tried to show you 5 lines of code and how can I rewrite those 5 lines using a move instructions to look more professional code.

In reality, There are 6 conveyors in total and I created UDT called "conveyor_control" and there is 6 parameter of this UDT.
1. Start sensor
2. Stop sensor
3. Start timer
4. Stop timer
5. motor run
6. Unmatched condition timer

Then I created conveyor array and used "conveyor_control" data type for that array and then I get conveyor[0] to Conveyor [7]

Now for conveyor 1, I am using followings tags

conveyor0.start_sensor
conveyor0.stop_sensor
conveyor0.start_timer
conveyor0.stop_timer
conveyor0.motor_run
conveyor0.Unmatched condition timer, this timer will turn ON when part present on conveyor 1 and no part present on conveyor two and conveyor 1 will stop when part reached at conveyor 2 but if someone picks up the part while traveling in between conveyor, so my part will never reach to conveyor 2 and my motor for conveyor 1 will never stop and this timer will stop the motor after 20 sec ( if average time to reach part is 10 seconds and motor continue to run )

But I agree with your points, I should use name more realistic like instead of using running bit, I will change to line run and so on. Thank you for the advice

I also liked your program strcutre and i will try to follow some of it and will implement some of my ideas but I would like to use AOI (add on instrcution) because it will make easy to troubhlshoot and change the code. I dont know how to use AOI but I am learning it and will change that code and update you guys!

Please let me know if you want to see my code? I will be at work tommorow and will send you my .ACD file.

Thank you again for your time and advice and sorry if i missed something!

Best,
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old Today, 12:18 AM   #25
janner_10
Member
United Kingdom

janner_10 is online now
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 338
It doesn't matter what code looks like, as long as it works (more or less)

If you want to help the next guy then comments, comments & more comments.
  Reply With Quote
Old Today, 07:50 AM   #26
LoganB
Lifetime Supporting Member
United States

LoganB is online now
 
Join Date: Apr 2017
Location: Michigan
Posts: 350
Be cautious with how you use AOIs. They are mainly used to protect parts of the code that you don't want people to see or change and they can't be edited online, so the code itself needs to be absolutely mistake proof.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old Today, 09:50 AM   #27
backendcode
Member
Canada

backendcode is online now
 
Join Date: Aug 2017
Location: brampton
Posts: 156
Quote:
Originally Posted by LoganB View Post
Be cautious with how you use AOIs. They are mainly used to protect parts of the code that you don't want people to see or change and they can't be edited online, so the code itself needs to be absolutely mistake proof.
I am going to stick with this code but I am just trying to learn AOI and I think this is the best way I can learn AOI in real project.

AOI for this project is for learning purposes and I will get back to my original code.

Thank you for giving me heads up on AOI.

Best,
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 2 (1 members and 1 guests)
RobertB
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
test the RSLogix500 code matches with PLC ?? leonlai LIVE PLC Questions And Answers 11 June 29th, 2011 12:41 PM
transfer data code from pc to omron plc ahmed yousri LIVE PLC Questions And Answers 0 March 13th, 2008 06:43 AM
Sub-routines - general question burnerman LIVE PLC Questions And Answers 25 March 2nd, 2006 09:56 PM
Protecting my code in Koyo products jimpad LIVE PLC Questions And Answers 12 September 4th, 2004 11:07 AM
How to simulate a FOR..NEXT loop? New2PLCs LIVE PLC Questions And Answers 26 May 9th, 2002 12:36 PM


All times are GMT -5. The time now is 10:03 AM.


.