Change Logix5000 Module IP in Run mode/ Dynamically

Hi,

I wonder if someone has done this already?

We are trying to change the IP address of a Generic Ethernet-Module dynamically using code in Run mode. We have two different data sources and the remote system (Gods Knows what it is) will tell us where to get data from by sending us the Source IP address. The Logix PLC (1756-L71) will set the new IP address for the generic Ethernet-Module and start receiving same data from different physical source.

The idea is Duty/Standby system...if one system is down the PLC will then receive data from standby system. The other option may be to configure Generic Ethernet Module for both data sources and use which ever is valid.

BUT

This will leave one module in connection fault all the time and will require extra work around to display correct status on SCADA for correct module and keep the name of module same etc.
  Reply With Quote
Old October 11th, 2017, 11:44 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,374
I've done things like this with robot end-effectors and exchangeable tooling.

As far as I know, you can't programmatically change the IP address of an I/O object in the I/O tree of ControlLogix.

For a system like the one you describe where there are only a few options, the straightforward solution is to put all the possible objects into the I/O tree.

You can either simply ignore the faulted I/O connections from the ones that aren't connected, or you can use SSV instructions to programmatically Inhibit or un-Inhibit them.
  Reply With Quote
Old October 12th, 2017, 03:13 AM   #3
whussain6
Member
United Kingdom

whussain6 is offline
 
Join Date: Oct 2013
Location: Newcastle
Posts: 87
Thanks Ken,

I was thinking the same i.e. to inhibit the module not required. I was just looking for neater solution.

What if the remote system uses DHCP so the IP address is not fixed? which is not my problem but just curious.

Could you help me find the Instance, Class, attribute etc for CIP Messages for Generic Ethernet Module? such as to read the IP configured for the modules in the IO tree?

I mean is there any document where I can find this?

Last edited by whussain6; October 12th, 2017 at 03:18 AM.
  Reply With Quote
Old October 12th, 2017, 12:03 PM   #4
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 1,915
I would recommend you to inhibit module that is not in use.
When you have a faulted connection, controller constantly trying to reestablish it, using an unconnected buffers.
There is a limit on these. More I/O you have faulted, more buffers will be used.
The same buffers used to send messages so you may see MSG instructions faulted time to time. There are other reasons not to load unconnected buffers.
  Reply With Quote
Old October 12th, 2017, 12:15 PM   #5
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 1,915
Quote:
Could you help me find the Instance, Class, attribute etc for CIP Messages for Generic Ethernet Module? such as to read the IP configured for the modules in the IO tree?
I mean is there any document where I can find this?
Starting with V24, you can read configured project Module path using GSV instruction.
From there you can extract IP address.

Reading the actual IP address from a remote module is possible but this is catch 22, because you need to specify IP address in the MSG instruction.
You probably need to configure DHCP persistence or static addresses instead.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
GE QuickPanel IP Address Change PLCPRO1 LIVE PLC Questions And Answers 1 April 20th, 2016 12:41 PM
Factorytalk view password reset button problem Nan LIVE PLC Questions And Answers 6 September 29th, 2015 01:16 PM
Micrologix 1100 memory module kolyur LIVE PLC Questions And Answers 5 June 24th, 2015 09:50 AM
What are the 3 processor modes? StoneNewB LIVE PLC Questions And Answers 8 March 22nd, 2015 07:13 AM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 06:38 PM


All times are GMT -5. The time now is 09:48 AM.


.