Old October 12th, 2017, 12:38 PM   #1
nick88
Member
United States

nick88 is offline
 
Join Date: Oct 2015
Location: West Virginia
Posts: 7
RS485 Communication Issue

I have a Redlion G315 HMI dsplay with a RS-232 serial communication link using an ABB TotalFlow Master driver. The RS-232 serial line is hooked to a B&B Smartworx RS-232/RS-485 isolated converter. 2-wire RS-485 link wired as a daisy chain is used to talk to three different nodes in the field. Total distance of communication link is probably around 600 ft or so. Im using a single pair shielded 16awg.

Each node is a Totalflow RTU. I do have the termination resistor jumper set on the last RTU. I am using the Redlion to poll app-array-registers out of the RTU's and display on the HMI.

I am able to poll the first RTU with no issue, but if I try polling the polling the second RTU, I loose communications. I do not receive any data from RTU's one or two.

What are some troubleshooting methods I can try to see whats going on?

Nick
  Reply With Quote
Old October 12th, 2017, 01:46 PM   #2
KuulKuum
Member
United States

KuulKuum is offline
 
Join Date: Jun 2006
Location: Texas
Posts: 104
Quote:
Originally Posted by nick88 View Post
I have a Redlion G315 HMI dsplay with a RS-232 serial communication link using an ABB TotalFlow Master driver. The RS-232 serial line is hooked to a B&B Smartworx RS-232/RS-485 isolated converter. 2-wire RS-485 link wired as a daisy chain is used to talk to three different nodes in the field. Total distance of communication link is probably around 600 ft or so. Im using a single pair shielded 16awg.

Each node is a Totalflow RTU. I do have the termination resistor jumper set on the last RTU. I am using the Redlion to poll app-array-registers out of the RTU's and display on the HMI.

I am able to poll the first RTU with no issue, but if I try polling the polling the second RTU, I loose communications. I do not receive any data from RTU's one or two.

What are some troubleshooting methods I can try to see whats going on?

Nick
Nick,
Is this a new installation or an existing one that used to work?
You also stated single pair shielded 16awg (is this "twisted" pair?) also is the signal grounded to a common ground?
Another idea is to provide terminating resistors at each extreme end of your communication link.
Check you communication settings (half duplex, baud rate, parity, etc.)
  Reply With Quote
Old October 12th, 2017, 06:09 PM   #3
danw
Member
United States

danw is online now
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,645
RS-485 does not like spurs. A spur is cabling which the tees off the main line and to connect to a node on multidrop network. Reflections will create comm issues. The main line network should connect to the node directly and then go onto the next node from the same node connection terminals.

Be aware that a lot of devices do not register or acknowledge changes in serial settings (baud rate, parity) unless the device is power cycled.

The cable should be twisted pair.

Comm cables should not run parallel to or in the same conduit/tray as power wiring.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Cimplicity 6.1 Communication Issue CP-5611 A2 kire LIVE PLC Questions And Answers 0 August 15th, 2017 08:08 AM
Simocode Pro V Communication Issue calvindodds@hotmail. LIVE PLC Questions And Answers 1 June 6th, 2017 05:41 AM
delta Rs485 communication muds LIVE PLC Questions And Answers 1 November 2nd, 2015 10:47 AM
RS485 Modbus Temp. Controller Issue Plutonius LIVE PLC Questions And Answers 0 August 2nd, 2014 08:01 AM
ML1400 Modbus RS485 Communication. rQx LIVE PLC Questions And Answers 15 March 17th, 2014 10:10 AM


All times are GMT -5. The time now is 09:56 AM.


.