I have a pair of fuji frenic mini c2 drives on exhaust fans, and I can't change any parameters.

F00 is set to 1

X1 is set to WE-KP

Jumper is on sink.

Tried to jumper x1 to cm and verified it with a meter. The drives are both on pad control and motors aren't running.
 
I was able to get there vendor out of him, finally. The drives come factory programmed and can not be changed. I posted here out of desperation as the clock was ticking, but it turns out this is some odd ball OEM ****.
 
While viewing F00, try holding stop while pressing the down arrow to change it to 0.
 
While viewing F00, try holding stop while pressing the down arrow to change it to 0.

I tried this as it was in the manual, but I can't remember if it was on F00 or not. These have to be integrated into a fire suppression system on a hood, so i'm done fiddling with them.
 

Similar Topics

Not a PLC question, but this is an excellent resource for information and has helped me tremendously over the years. Need to replace an old Fuji...
Replies
3
Views
1,778
What is the latest replacement available for a Fuji FRENIC drive # FRN075G9D-4UX? I have replaced one with a G11 series, but that was years ago...
Replies
1
Views
1,762
Anybody have any experience with the Frenic Mega VFD's PID feature? Today I was trying to modify a customer's setup with less than spectacular...
Replies
2
Views
1,225
Does anyone have any experience using a Profibus interface to a GE Fuji variable frequency drive? We have limited experience communicating from a...
Replies
4
Views
7,098
Hi Anyone know what the pinouts on the control (ie start/stop etc etc) plug is on a Fugi Invertor FMD 5AN 21 This is a unit from a Fanuc CNC...
Replies
4
Views
4,916
Back
Top Bottom