Data Store Plus to Network

janner_10

Lifetime Supporting Member
Join Date
Dec 2014
Location
Tewkesbury
Posts
1,301
I am successfully logging to a network location with a PV+ 7.

However, every time the project starts after a reboot, I get presented with this screen, despite the Network Identification settings being filled out in the Terminal Settings.

The additional downside is that the inputs dont bring up the keyboard so you have to use a USB keyboard or access via VNC

rck9wm.png


Anyone have any ideas?
 
I think you need to save the registry; but I thought the PV+7 did that automatically.
Could be a bug.

Anyway, to be sure, make your Network Identification setting changes.
Open the command prompt and run regflush (if that's even still there).

The PanelViewPlus runs in RAM for all of its memory. It needs to manually save any changes (ex. Registry) back to the internal storage before a power cycle. Maybe that part is not working; a bug on PV+ 7.
 

Similar Topics

Hello friends, i want to store trends value data graphically in panel view plus 7 standard HMI & scroll back to see trends is it possible...
Replies
2
Views
1,709
I am currently spending a nice couple of days on the Emerald Isle, doing a startup. However, the customer can't make up his mind to the frequency...
Replies
2
Views
1,704
Hi all, I have an application where I want to log batch details to a file after each batch using a PanelView Plus 6. The PLC is a Compact Logix...
Replies
17
Views
8,238
Hello all, I'm using a 5069-L330ER in a project and I need to essentially capture some data that will be shown as a trend on a screen. The data...
Replies
9
Views
941
Hello all first time user here with a question about how to repopulate data on my controllogix 5561 176-L61B. Combination of a low PLC battery and...
Replies
7
Views
975
Back
Top Bottom