GX Works3 and FX5U Ladder Sequencing

lgray66

Member
Join Date
Mar 2009
Location
Ohio
Posts
3
Hello,
I'm new to Mitsubishi, but not to PLC programming. I have converted a program we've used on AB, Siemens, and Automation Direct to the FX5U; and the attached rungs do not work. Basically, it just zeros a variable, then adds a number to it based a bit. It is as if it is only executing the MOV and not the ADD. I thought maybe it was just the monitoring was not displaying it correctly, but the routines that follow are not executing. I've also attached the same routine from Siemens, showing the ADD working. Is there something I need to do differently in GX Works3? Has anyone else seen this behavior?

S7-1200 Add.jpg FX5U Add.png
 
hello,


MOVE after SM400 will write 0 to D40 in every scan


ADDP_U is PULSE controled instruction, so written value will stay in D40 only for one scan
 

Similar Topics

Hi everybody, First time with gxworks 3 and it take a little getting use to. I have been skimming the manuals and writing my programs for the...
Replies
14
Views
3,127
Hi Guys, Who amongst us has worked on Mitsubishi FX5U with Analog extension modules and GX Works3? Please, I will need your support here...
Replies
0
Views
907
Hello, As a newbie to PLCs, I have two issues. 1) I connected Mitsubishi GX Works3 and Factory IO on a project I am working on. But when I do a...
Replies
2
Views
1,864
Hi, I have setup the Simple PLC communication in RJ71C24 (Channel 2) for communication between Mitsubishi IQ-R series PLC (Mosbus RTU Master) and...
Replies
4
Views
2,490
A cry for help to parky and Mitsubishi gurus. How do you confirm the firmware version of the iQR PLC or a module such as the RJ71GN11-T2? I have...
Replies
3
Views
1,018
Back
Top Bottom