communication in iNTOUCH

eseq

Member
Join Date
Apr 2006
Location
Legnica
Posts
12
Hello all!
I speak english a little:) I have problem, because I can't understood communication between STEP 7 and Intouch. The name of the variables in the intouch isn't the same in Step 7, therefore how does it communication with step 7?
 
The variables in the SCADA will have numbers attached to them. This is what the PLC recognises - the variable names in InTouch are irrelevant.
 
but how to link value, which is actual posizion in step 7"db1.dbw0" whit tagname "table" in Intouch?
 
Cannot help you with Siemens but would suggest check the InTouch help files where word/bit types should be defined.
 
You have probably already solved...

In siemens address is DB7.DBW0 to access in Wonderware the address is DB7,W0
Siemens: DB7.DBX2.4 would be in
Wonderware: DB7,X2.4
and so forth....
 

Similar Topics

hi everyone. i hope you guys are doing great. i am trying to built communication between aveva intouch hmi 2023 and tia portal v18. i dont have...
Replies
1
Views
537
Hi All Predictably, I have a problem making Intouch talk to compactlogix 5380 plc !!! In Intouch I've declared : Access name = Tank_Farm Node...
Replies
0
Views
696
Hi AllN Predictably, I have a problem making Intouch talk to compactlogix 5380 plc !!! In Intouch I've declared : Access name = Tank_Farm Node...
Replies
13
Views
3,092
I apologize in advanced if this has been answered before but I was unable to find an answer searching the forum. I have Wonder InTouch on a PC...
Replies
9
Views
6,263
Hi Everyone I had to replace an HMI & the project Intouch 7.11 was converted to Intouch 2014 R2 SP1 version. The PLC is TSX Premium. Installed...
Replies
0
Views
962
Back
Top Bottom