Help for Guard Logix CPU L71S

Ali Raza

Member
Join Date
Oct 2016
Location
Lahore
Posts
16
Help required For Guard Logix CPU L71S

We are facing following problems for gurad logix

1) How we can edit the safety Program and safety tags

2)Could not change the Safety Modules Properties

Is there is any procedure for that or it is software end Problem using Studio 5000 standard edtition

After that we send Empty program with Existing Hard ware then At online it gives I/O Not OK communication not established bw EN2tr to AENTR and its safety point ios
 
You have to unlock the safety to change anything safety related....in the upper left of logix while online does it show locked or unlocked?
 
You can't modify any safety programs using Logix Standard Edition. You will need Full or Professional edition.

And, as robertmee said, you'll have to have the safety unlock password too.
 

Similar Topics

Hello, I'm adding an Allen-Bradley SensaGuard door switch (440N-Z21SS2H) to a small existing machine to drop out pneumatic function when the...
Replies
3
Views
899
Hi to the forum. I have a logic problem which is confusing me. From my sketch I have seven conveyors that I control using a twido PLC via canbus...
Replies
19
Views
5,591
Hi, We have an application that has a device that goes through a reboot (appears un-graceful) What then happens is the MVI module appears to hang...
Replies
0
Views
51
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
493
Hi all, i am the new controls guy at the plant and i have inherited a pc from the previous controls guy with Siemens tia portal version 16 and 17...
Replies
15
Views
459
Back
Top Bottom