Output Forces in ControlLogix

mckeeal

Member
Join Date
Jun 2007
Location
East Texas
Posts
1
I have a ControlLogix processor, V13 firmware.

I am able to force the inputs with no problem. The outputs will not force, either from the ladder or the data table.

Anybody seen this before??

thanks,

alan
 
You have to realize how forcing works in Allen-Bradley PLCs. When you force the output, you affect the "physical" output only. So if you force an output wired to a light, the light will energize. This has NO effect on your ladder logic. You will not "see" any change in the logic window.

Other than that, there is no difference in forcing inputs versus outputs.

Keep in mind also, that you can only force real outputs or aliases to real outputs. If it is internal, it won't work.

Also... make sure that you are looking at the output tag. For example:

Local:2:I.Data.5
Local:2:O.Data.5

Both examples are valid addresses for an output module in slot #2 of the local chassis. The first is simply reading what the output was told to do, whereas the second is telling the output what to do.

OG
 

Similar Topics

How can I use 1 button and 1 light using only b3
Replies
5
Views
57
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
5
Views
35
Hello guys, I am new to this forum and have some problems with my PowerFlex755 EENET frequency inverter. I want to do a point to point...
Replies
0
Views
32
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
Replies
1
Views
60
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
1
Views
111
Back
Top Bottom