Timer on delay in rung

Hey guys

So this is one of those things that siemens really does better then AB.

Im trying to find a work around for it.

I want to use a simple timer in a rung. But i want to actually place the timer in the rung it blocks.

NOT put the timer in some other rung and use a contact tied to its done bit.

In siemens land this is very normal. A block in siemens with several outputs can have the outputs physically tied to the rung.

AB will not allow this.


How can i get around this or make an AOI that does.

For example, in AB the only thing on a TON instruction that can be tied to the rung is the enable. What im trying to do is get the DN tied to the rung instead

Any ideas????
  Reply With Quote
Old December 6th, 2018, 11:48 AM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,628
Is there a reason why the tried and true method isn't acceptable for your case? One of the typical sources of frustration for a person trying to learn a new platform comes when they try to make the new platform behave like the one they're already familiar with.
  Reply With Quote
Old December 6th, 2018, 12:00 PM   #3
rscott9399
Member
Norfolk Island

rscott9399 is offline
 
Join Date: Aug 2017
Location: in space
Posts: 86
Quote:
Originally Posted by Steve Bailey View Post
Is there a reason why the tried and true method isn't acceptable for your case? One of the typical sources of frustration for a person trying to learn a new platform comes when they try to make the new platform behave like the one they're already familiar with.

I understand your point.

However, i wouldn't say im learning AB. I know both

I am just sick and tired of having timers all over the place with contacts also all over the place instead of having one nice neat block that allows the rung to go hot when it completes without having to have a timer somewhere else also.
Its messy and hard to follow.
  Reply With Quote
Old December 6th, 2018, 12:08 PM   #4
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,628
Quote:
Its messy and hard to follow.
Even when the next rung in the program following the timer is controlled by the timer's .DN bit?
  Reply With Quote
Old December 6th, 2018, 12:18 PM   #5
rscott9399
Member
Norfolk Island

rscott9399 is offline
 
Join Date: Aug 2017
Location: in space
Posts: 86
Quote:
Originally Posted by Steve Bailey View Post
Even when the next rung in the program following the timer is controlled by the timer's .DN bit?
In my opinion yes,
  Reply With Quote
Old December 6th, 2018, 12:34 PM   #6
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 942
Quote:
Originally Posted by rscott9399 View Post
In my opinion yes,
Opinions are like *******s... everyone's got one, but sometimes you shouldn't flash it around in public.

I simply branch around the timer which being an "output" type instruction sits on the far right of the rung, with the .DN bit in an XIC, followed by the coil which this rung of timer related logic is turning on.

Keeps it all together and it looks tidy, in my opinion (whoops, there's that dirty word again!).
  Reply With Quote
Old December 6th, 2018, 12:35 PM   #7
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,307
Put a branch below the timer. Run that off the .DN bit.
Done.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old December 6th, 2018, 12:53 PM   #8
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 667
Keep it neat if its a TON

Contact - Timer - Contact.DN - Coil
  Reply With Quote
Old December 6th, 2018, 09:03 PM   #9
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 429
Maybe I'm misunderstanding, but since RSLogix 5000 came out in the late 90s you can have mutiple outputs in series on the same rung. So you can have a TON instruction followed by a .TT or .DN bit in the same rung.

TON My_Timer XIC My_Timer.DN OTE My_Output

Or are you using some AB software designed in the 80s?

Last edited by rupej; December 6th, 2018 at 09:06 PM.
  Reply With Quote
Old December 7th, 2018, 08:41 AM   #10
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 514
Quote:
Originally Posted by rupej View Post
Maybe I'm misunderstanding, but since RSLogix 5000 came out in the late 90s you can have mutiple outputs in series on the same rung. So you can have a TON instruction followed by a .TT or .DN bit in the same rung.

TON My_Timer XIC My_Timer.DN OTE My_Output

Or are you using some AB software designed in the 80s?
Was going to say this as well. In some of our alarming logic we have TONs with their .DN bit in sequence right after the timer. The timer will start when the permissives to the left of the timer are all true, but everything beyond (to the right) of the timer will remain false until the timer completes and the DN bit turns on.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old December 7th, 2018, 11:22 AM   #11
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 206
In AB Ladder, the only thing that gets tied to the output of a block is a hidden "EnableOut". Since in a TON instruction, this is logically equivalent to the EnableIn, which is the same as the .EN element, they display the instruction as if it were connected to a -(EN) coil.

For other blocks -- MOV, ADD, etc., there is no logical equivalent, so the "output" of the block is nothing.

Now, if you want to be able have branches start INSIDE the block (i.e., a branch off the EN, another off TT, and another off DN), then you need to use the TONR and do function block programming, not ladder.

Alternatively, you could create an AOI with a single line of ladder:
XIC EnableIn TON Timer XIC Timer.DN OTE EnableOut
and add a "PRE" input parameter that is aliased to Timer.PRE and has the VIS box checked. Same with an "ACC" output parameter to Timer.ACC

Since you are now driving the EnableOut bit based on the .DN, you'll get what you're looking for.
  Reply With Quote
Old December 7th, 2018, 01:10 PM   #12
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 514
Quote:
Originally Posted by Aardwizz View Post
In AB Ladder, the only thing that gets tied to the output of a block is a hidden "EnableOut". Since in a TON instruction, this is logically equivalent to the EnableIn, which is the same as the .EN element, they display the instruction as if it were connected to a -(EN) coil.

For other blocks -- MOV, ADD, etc., there is no logical equivalent, so the "output" of the block is nothing.

Now, if you want to be able have branches start INSIDE the block (i.e., a branch off the EN, another off TT, and another off DN), then you need to use the TONR and do function block programming, not ladder.

Alternatively, you could create an AOI with a single line of ladder:
XIC EnableIn TON Timer XIC Timer.DN OTE EnableOut
and add a "PRE" input parameter that is aliased to Timer.PRE and has the VIS box checked. Same with an "ACC" output parameter to Timer.ACC

Since you are now driving the EnableOut bit based on the .DN, you'll get what you're looking for.
Is there any meaningful benefit to do it this way vs just having the .DN bit in series after the timer? Or is it just a useful way to do more complicated actions as well?
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old December 7th, 2018, 01:25 PM   #13
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 206
Quote:
Originally Posted by LoganB View Post
Is there any meaningful benefit to do it this way vs just having the .DN bit in series after the timer? Or is it just a useful way to do more complicated actions as well?
Essentially, it's useless. The OP was insisting that AB work like he's used to with Siemens, where he could drop a timer block on a rung and have the output of the block not be "hot" until the timer is done.

Putting the DN contact after a TON on the same rung does the same thing, and is clearer as to what is going on. Conditionally driving the EnableOut bit is just weird.
  Reply With Quote
Old December 7th, 2018, 01:35 PM   #14
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 514
Quote:
Originally Posted by Aardwizz View Post
Essentially, it's useless. The OP was insisting that AB work like he's used to with Siemens, where he could drop a timer block on a rung and have the output of the block not be "hot" until the timer is done.

Putting the DN contact after a TON on the same rung does the same thing, and is clearer as to what is going on. Conditionally driving the EnableOut bit is just weird.
Gotcha, thanks!
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
on delay timer as a universal timer aftab_khan LIVE PLC Questions And Answers 4 April 18th, 2018 11:09 AM
OFF Delay Timer in QnA Series rajivs1107 LIVE PLC Questions And Answers 3 February 27th, 2010 12:51 PM
SLC logic not solving as expected...seen this before<?> jdbrandt LIVE PLC Questions And Answers 11 November 6th, 2008 09:30 AM
Rslogix5 plcdb222 LIVE PLC Questions And Answers 21 September 29th, 2006 10:32 AM
Random delay timer Philippe LIVE PLC Questions And Answers 1 July 4th, 2003 08:04 PM