Rockwell CCW and 5370 Controller issues

Hi all,

Hope all is well with you and yours.

Ok, so here is the deal.

I have a 1769-L33ER (5370) Controller with 31.x firmware loaded.
I can program it just fine using Studio 5000.
I'm connected to it using the USB port in front of the controller
I'll be using the Ethernet for communications

I want to connect a HMI Panelview 800-T4T using the USB port to the PLC

So I install the Connected Components Workbench v11.x

When I try to select the controller, which I do see on the communications paths (USB, same one as I use on the studio 5000), it just keeps saying "Failed to connect to device. Verify the connection is active and device is supported".

Okay, so I saw that there is a patch for the 5370 controllers and CCW, so I installed that. Same issues.

When I go to the controller "settings", and try to select the controller type, all it shows is "Micro800", I cannot locate "5370"...

The protocol I've selected is "Serial | Allen Bradley CIP"

Again, I want to use the USB port to connect the HMI, and I'll be using the Ethernet for the backend PLC software...

Any advice would be greatly appreciated.

~Kam
  Reply With Quote
Old November 13th, 2018, 12:53 PM   #2
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,484
What is the firmware revision of the PanelView 800 terminal?...

In order to communicate with a 5370 L1 controller, the PanelView 800 terminal must be at firmware revision 3.011 or higher.

In order to communicate with a 5370 L2 or L3 controller, the PanelView 800 terminal must be at firmware revision 4.012 or higher.

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old November 13th, 2018, 12:57 PM   #3
Kamputty
Member
United States

Kamputty is offline
 
Join Date: Nov 2018
Location: Santa Cruz
Posts: 14
Hi George,

Thanks for the fast reply.

Currently, I do not have the Panelview connected. I'm using the CCW software to create a project and interact with the PLC...the project can "see" the USB communications path, but alas, when I select, I get the error I listed.

~Kam
  Reply With Quote
Old November 13th, 2018, 01:25 PM   #4
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 595
CCW will not program controllogix or compactlogix plc's.
__________________
David M. Camp

Marshall Electric / https://mei-tech.com/monitor-and-control

Please Download from our download section "Monitor and Control" .pdf.
  Reply With Quote
Old November 13th, 2018, 01:32 PM   #5
Kamputty
Member
United States

Kamputty is offline
 
Join Date: Nov 2018
Location: Santa Cruz
Posts: 14
Hi David,

I'm not programming the controller using CCW, for that I'm using Studio 5000.
What I'm doing is trying to create a HMI screen...for the 4" panelview...

next step for me is to change the connection path from USB to ethernet and see if that helps...
  Reply With Quote
Old November 13th, 2018, 01:45 PM   #6
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,889
Not sure I completely understand but... why dont you use the Ethernet ports on both?

EDIT: All three for that matter, PC, HMI and L33er
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old November 13th, 2018, 01:51 PM   #7
Kamputty
Member
United States

Kamputty is offline
 
Join Date: Nov 2018
Location: Santa Cruz
Posts: 14
I'm doing that right now...seeing if the issue is that the CCW software does not work with the USB...
  Reply With Quote
Old November 13th, 2018, 02:13 PM   #8
Kamputty
Member
United States

Kamputty is offline
 
Join Date: Nov 2018
Location: Santa Cruz
Posts: 14
okay, removed the USB path.

PLC IP = 192.168.1.10

My laptop = 192.168.1.100

both connected via a switch.

I can program and "see" the PLC 100% fine using the new ethernet path with Studio 5000.

When I run the CCW, I "see" the path, when I select the path, it says the same thing...

So, USB is removed. Same issue.

Thoughts?

~Kam
  Reply With Quote
Old November 13th, 2018, 03:56 PM   #9
JordanCClark
Lifetime Supporting Member
United States

JordanCClark is offline
 
JordanCClark's Avatar
 
Join Date: Mar 2007
Location: Michigan
Posts: 487
The USB port on the PLC is not meant for anything except programming the PLC. Use ethernet.

What IP address is set on the HMI?

How is your communication driver set up in CCW?
__________________
_____________________________
Jordan

Any man that can hitch the length and breadth of the Galaxy, rough it, slum it, struggle against terrible odds, win through and still know where his towel is, is clearly a man to be reckoned with.
-- Hitchhiker's Guide to the Galaxy
  Reply With Quote
Old November 13th, 2018, 04:11 PM   #10
Helliana
Member
United States

Helliana is offline
 
Join Date: Nov 2011
Location: Arkansas
Posts: 606
You must use Ethernet for communication between the PLC and HMI. The USB ports on both are for programming only.


The communication drivers for the HMI should be set in CCW as follows:

Protocol: Ethernet | Allen-Bradley CompactLogix
Controller Type: CompactLogix 5370
Address: 192.168.1.10,1,0


That is assuming your ip address of your PLC is 192.168.1.10. You must add the ,1,0 at the end of the address. Also, make sure the firmware the most current version available. I'm using currently using version 5.011.
  Reply With Quote
Old November 13th, 2018, 04:13 PM   #11
Kamputty
Member
United States

Kamputty is offline
 
Join Date: Nov 2018
Location: Santa Cruz
Posts: 14
Hi Jordan,

Okay, here is my setup for clarity.

PLC = 1769-L33ER
HMI = 2711R-T4T

PLC IP = 192.168.1.10
Computer IP = 192.168.1.50
HMI IP = NOT SETUP

My Computer and PLC are connected via Ethernet (USB works fine too).
I can program and "talk" to the PLC just fine using the Studio 5000.

Now I want to create my first HMI project, so I installed CCW.

Keep in mind, the PHYSICAL HMI is still not connected to anything.

When I run CCW, I "see" the communications paths to the PLC. When I select either the Ethernet or USB (both work fine in Studio 5000), I get the "invalid error"...

Again, I have NOT wired the HMI into anything, and looking at the tutorials, I would not need to when I'm creating the HMI project...

Thoughts?

~Kam
  Reply With Quote
Old November 13th, 2018, 04:27 PM   #12
JordanCClark
Lifetime Supporting Member
United States

JordanCClark is offline
 
JordanCClark's Avatar
 
Join Date: Mar 2007
Location: Michigan
Posts: 487
Quote:
Originally Posted by Kamputty View Post
When I run CCW, I "see" the communications paths to the PLC. When I select either the Ethernet or USB (both work fine in Studio 5000), I get the "invalid error"...
This is the part I don't understand. You don't need to connect to the PLC to make your projects either.
__________________
_____________________________
Jordan

Any man that can hitch the length and breadth of the Galaxy, rough it, slum it, struggle against terrible odds, win through and still know where his towel is, is clearly a man to be reckoned with.
-- Hitchhiker's Guide to the Galaxy
  Reply With Quote
Old November 13th, 2018, 04:28 PM   #13
Helliana
Member
United States

Helliana is offline
 
Join Date: Nov 2011
Location: Arkansas
Posts: 606
I can't follow what you are attempting to do. You don't have to do ANYTHING to the PLC in CCW, other than setup the communications tab in the HMI configuration.

Last edited by Helliana; November 13th, 2018 at 04:45 PM.
  Reply With Quote
Old November 13th, 2018, 04:31 PM   #14
Helliana
Member
United States

Helliana is offline
 
Join Date: Nov 2011
Location: Arkansas
Posts: 606
Attached is a screenshot of my CCW setup with a Panelview800 talking to a L24 CompactLogix.
Attached Images
File Type: png CCWcap.PNG (79.8 KB, 99 views)
  Reply With Quote
Old November 13th, 2018, 06:36 PM   #15
Kamputty
Member
United States

Kamputty is offline
 
Join Date: Nov 2018
Location: Santa Cruz
Posts: 14
Thanks for the screen shot. My project looks just like that.

My IP is 192.168.1.10,1,0

Now the issue is with tags!

This is what I am doing regarding tags...

I have a TAG on the PLC called "RUNTIME_STATUS_EXTERNAL" that is "PUBLIC" "DINT".

I create a TAG on the HMI with the following --

Tag Name: RUNTIME_STATUS_EXTERNAL
Data Type: 32 bit int
Addess: RUNTIME_STATUS_EXTERNAL
Controller: PLC-1

I created a Numerical Display, with the "READ TAG = RUNTIME_STATUS_EXTERNAL", and the "Visibility Tag = RUNTIME_STATUS_EXTERNAL"

When I load the HMI, I get the following error on the HMI side...

"2: Data Access Error for Alias RUNTIME_STATUS_EXTERNAL, Controller PLC-1, Address RUNTIME_STATUS_EXTERNAL, Communications Flag i*"

Right now, everything is via Ethernet.

PLC = 192.168.1.10
HMI = 192.168.1.20
PC = 192.168.1.50

~Kam
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 01:07 PM.


.