plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old January 24th, 2023, 07:40 AM   #1
sbaum
Canada
sbaum is offline
Touch / Continuity Sensing
Looking for some ideas on sensing contact between 2 metal parts.
The application is a part gauge fixture. The gauge and part are both conductive metals. There is an aluminum test tool that is isolated from the rest of the gauge. We need to sense if that tool comes in contact with the part and turn on a light.
We have been using Omron D5C-1DA0 touch sensors for this. Works reasonably well, although can be a bit sensitive to set up. These sensors are now being discontinued so we're looking for another solution.
The toolmaker's suggestion has been to use a 5vdc source to a relay coil. Could connect the 0vdc to the fixture chassis and run the 0vdc of the relay coil to the isolated tool. Of course this would work but in my view this is a shock hazard for the operator when loading the part. Unless there's a way to limit the current to <1mA. (Still don't know what my electrical inspector would say)
Seems there must be a solution on the market for this but I've search several industrial sensor suppliers and so far no success.
Old January 24th, 2023, 10:30 AM   #2
joseph_e2
United States
joseph_e2 is offline
I've seen these in use for something similar:
https://www.se.com/us/en/download/document/6008346/
https://tesensors.com/global/en/prod...erence/ST08164
I'm not sure if they're still available or not, but I remember buying some as recently as 2016 or so. With Schneider having bought Telemecanique who appears to have bought R.B. Denison, support may be spotty. And there isn't a whole lot of info on their website, but I've attached a slightly better datasheet that I had saved.
One application was detecting when a metal part reached a gate on a conveyor. The gate was plastic with 2 metal pads that the part would bridge. Another application was as a jam-up detector. The stack of parts would buckle, contacting a plate above them which would cause the switch to close.
Old January 24th, 2023, 11:20 AM   #3
5618
United States
5618 is offline
5618's Avatar
They're marketed for level sensing of conductive liquids, but if you have a dry process maybe you could use something from Warrick Controls to detect conductivity when parts touch.
https://www.gemssensors.com/product/...ivity-controls
Edit: I would consider 16MA... for low value 4.7K threshold. I don't think you would need something high like 1M ohms. Another one to consider is 16VM... for field settable threshold if you want to try different settings.
Old January 24th, 2023, 12:45 PM   #4
sbaum
Canada
sbaum is offline
Thanks for the suggestions so far.
I'd prefer 24VDC controls but the Telemecanique unit is close to what I'm looking for. Now will need to see if available...
I had also thought of the Warrick Controls units. I may need to investigate those further as well.
Old January 24th, 2023, 01:06 PM   #5
joseph_e2
United States
You might also reach out to Keyence. Just be prepared to hear from them pretty frequently afterwards...
Old January 24th, 2023, 07:01 PM   #6
I_Automation
United States
I_Automation is offline
I_Automation's Avatar
I have used level sensors designed for 3 probes in liquid. You can jump the Low level terminal to COM probe terminal and wire almost anything between COM & High that will give you a relay output.
The sensors put out a safe signal that doesn't energize the fluid it's in and is safe to the touch.
__________________
ivanovaautomation.com
Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
Old January 24th, 2023, 10:34 PM   #7
rdrast
United States
rdrast is offline
rdrast's Avatar
Around here, I just tie the 'Sensor' part to +24VDC through a 2.2K pull-up resistor, and also tie the 'Sensor' part to a PLC Digital input. The product is grounded through the machine frame.
It is normally high, but goes to low if the product touches the sensor at all.
__________________
Old January 25th, 2023, 07:29 AM   #8
sbaum
Canada
sbaum is offline
This solution is attractive but I question the safety in my application as the operator is in direct contact with the part. There's 10mA current available between the 'Sensor' and the frame. (1mA can be felt, >6mA can cause loss of muscle control per OSHA)
Old January 25th, 2023, 02:04 PM   #9
I_Automation
United States
Quote:
The operator will only be in contact with the grounded 0V, and the operator creating contact between ground and the object tied to the 0V side of a relay contact will not feel anything from the 24VDC power supply.
I have even seen older systems using the ground the same for 120V coils without anyone getting zapped
__________________
Old January 26th, 2023, 02:16 PM   #10
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
I've seen it done with 24 volts and a resistor and with liquid level relays like this:
https://www.automationdirect.com/adc...ers/clc1-d-120
I prefer the liquid level relay because a resistor on a terminal block is sometimes problematic if it gets messed with or lost during repairs and the liquid level relays use low voltage and a very low current.
The one in my link is "5 volts DC pulsed".
The liquid level relays also have a sensitivity pot, so if things get grungy and give a false positive, or fail to detect contact, you can adjust them easily.
__________________
You've been taken, but you don't know it yet.
Old January 26th, 2023, 03:09 PM   #11
KingPresident
United States
KingPresident is offline
Quote:
LOL.
I had to catch my breath after that one!
Old January 26th, 2023, 04:00 PM   #12
joseph_e2
United States
Quote:
Originally Posted by KingPresident View Post
LOL.
We actually use a fair amount of their products, so I've managed to "train" them that I'll reach out when I need help. It took a bit, though...
Old January 26th, 2023, 07:40 PM   #13
I_Automation
United States
I have a lot of respect for my Keyence guy. Calls ahead and asks to schedule a visit if going around with someone from national or international, doesn't flood me with spam, etc. And does help out.
Now Cognex? I won't login to their website or download any datasheet or catalog. Plus especially do not respond to the 3 times weekly emails to win a free vision system.
They now have you in their database and will try to get to you every way they can - email, call, show-up at your office, show-up looking for you anywhere they find out you are going.
I will not spec Cognex components in any quote and if a customer requests Cognex I try to find a compatible product from another source or tell them they have to buy the Cognex stuff themselves.
__________________
Reply
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
problem in touch panel (ESA,505w) harrydeharry LIVE PLC Questions And Answers 7 August 24th, 2017 05:48 AM
PView+ 700 (Touch and Keypad) Disabling Touch? dipan LIVE PLC Questions And Answers 3 July 25th, 2016 10:32 AM
Why do industrial panel manufacturers use resistive touch ? JesperMP LIVE PLC Questions And Answers 18 May 9th, 2014 06:28 AM
broken Touch screen of C7-635 Touch control_eng2001 LIVE PLC Questions And Answers 5 June 25th, 2009 05:54 PM
CP340 communication with proface touch screen sttchui LIVE PLC Questions And Answers 1 September 3rd, 2008 03:39 AM