UPS in a PLC system

Looking for a UPS that integrates well into a L8xE Control logix installation.

We have used the AB 1609-D1500N Ethernet IP UPS's in the past, but they are now discontinued.

Would like to be able to pull UPS status and alarms into the PLC for HMI visibility.

Smaller 120VAC control probably less than 3KVA.
  Reply With Quote
Old February 3rd, 2023, 03:51 PM   #2
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,575
There are modbus option cards for many UPS that would work for this.
__________________
. . .Nostalgia used to be so much better . . .
  Reply With Quote
Old February 3rd, 2023, 04:27 PM   #3
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 2,100
I use APC Surta or APC SRT UPS and also Falcon Electric.
Get the IO module, you can get UPS status form them.
I use UPS (1500 to 2000) to supply power to the whole control system.

If you want less power... Phoenix Contact Quint supports Ethernet IP.
https://www.phoenixcontact.com/en-us...c20eip-2907074
__________________
****Control Freak****
Net is where I be and Nathan is me.
I have a condition called "The Knack".
https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s

Last edited by NetNathan; February 3rd, 2023 at 04:36 PM.
  Reply With Quote
Old February 3rd, 2023, 10:11 PM   #4
busarider29
Lifetime Supporting Member
United States

busarider29 is offline
 
Join Date: Aug 2013
Location: Midland, MI
Posts: 354
Beckhoff has a few models available that have digital I/O for the various UPS status, alarms, etc., so you can use them in non-Beckhoff applications. Power input is via your 24VDC power supply. We use them in all of our machines.

CU8110-0060
CU8110-0120
CU8130-0120
CU8131-0240
C9900-U330
C9900-U332
  Reply With Quote
Old February 4th, 2023, 11:59 AM   #5
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,575
netnathan
How you like the Falcons? I deployed several but they are too young to evaluate. I bought them for their temp range but their Modbus was some 3rd party dongle kind of thing so I didn't opt for it. If you did, how is it?
__________________
. . .Nostalgia used to be so much better . . .
  Reply With Quote
Old February 4th, 2023, 02:07 PM   #6
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 2,100
Quote:
Originally Posted by TheWaterboy View Post
netnathan
How you like the Falcons? I deployed several but they are too young to evaluate. I bought them for their temp range but their Modbus was some 3rd party dongle kind of thing so I didn't opt for it. If you did, how is it?
I like the Falcons a lot. Very fast delivery and support. Pretty durable, I have a few that have been installed for 3 years. The display is a little odd and takes a little understanding, but it looks cool. It would be nice if info was a little more straight forward, but the graphic display is universal language...

The strange thing I recently found out with them was the UPS does not like grounded neutral on the output?? I had to add a transformer on the supply side of the UPS to supply ungrounded 120V power to the primary of the transformer (from the UPS) and my controls on the secondary with a grounded neutral.
The oddest thing is The other 3 Falcons out there are running fine on grounded neutral from UPS.
__________________
****Control Freak****
Net is where I be and Nathan is me.
I have a condition called "The Knack".
https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s

Last edited by NetNathan; February 4th, 2023 at 02:16 PM.
  Reply With Quote
Old February 4th, 2023, 03:33 PM   #7
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,575
Yea, that display is indeed odd, a very Jetsons vibe to it.

All mine are grounded neutral and I have not seen that problem. Did have one where that E-stop contact was not jumpered. that was fun.
__________________
. . .Nostalgia used to be so much better . . .
  Reply With Quote
Old February 4th, 2023, 07:13 PM   #8
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 2,100
Quote:
Originally Posted by TheWaterboy View Post
Yea, that display is indeed odd, a very Jetsons vibe to it.

All mine are grounded neutral and I have not seen that problem. Did have one where that E-stop contact was not jumpered. that was fun.
By E-Stop, you mean the "Remote Emergency Power Off (REPO)"? I use that to shut down the UPS when control power is turned off.
I also use the UA88376-SSG board to allow remote monitoring of the unit by the plc and also a hardwire kit to remove the inlet/outlet plugs.
__________________
****Control Freak****
Net is where I be and Nathan is me.
I have a condition called "The Knack".
https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC Update - Back Issues Collection Now Available! Phil Melore LIVE PLC Questions And Answers 11 October 22nd, 2015 03:17 AM
Automated Parking System Using OMRON PLC and HMI kannan_kathiresan LIVE PLC Questions And Answers 196 October 13th, 2014 06:35 AM
How to reset the B&R system 2005 PLC Henry Siswant LIVE PLC Questions And Answers 1 February 20th, 2013 04:15 PM
Dcs, Scada hasnoclue LIVE PLC Questions And Answers 15 April 11th, 2005 07:12 AM
Generator Engine Control CaseyK LIVE PLC Questions And Answers 28 January 31st, 2005 09:56 PM


All times are GMT -4. The time now is 10:18 PM.


.