Old January 15th, 2011, 01:09 PM   #1
harrydeharry
Member
India

harrydeharry is offline
 
Join Date: May 2008
Location: Delhi
Posts: 237
problem in touch panel (ESA,505w)

Dear All,

I am facing problem in touch panel of ESA{505W,v 1.17,Italy}. Problem is that when I touch some buttons on screen it doesn't sense the touch. Also when numeric keypad got dispaled on screen and say I touch key "5" then "4" gets pressed which just placed on L.H.S of "5", same when "9" then "8" got pressed.
I feel that it may be the problem of calibration of Touch screen, but I don't how do it.Also I don't have any backup of it.

Please help and yes thanks in advance.

Regards.
  Reply With Quote
Old January 17th, 2011, 11:47 AM   #2
tracer
Member
United States

tracer is offline
 
tracer's Avatar
 
Join Date: Nov 2003
Location: Near Dallas Tx
Posts: 63
try cleaning the screen, if dirt / food gets on a screen and dries it can make it press into the screen enough to activate that section. other then that it's possinle to wear out a portion of the screen in which case you'll have to replace it and/or have it repaired.
  Reply With Quote
Old January 18th, 2011, 12:13 AM   #3
harrydeharry
Member
India

harrydeharry is offline
 
Join Date: May 2008
Location: Delhi
Posts: 237
But sreeen looks physically in good condition and clean srceen.
Please tell me the procedure of caliberation of screen and also which software is required for taking the backup.

Regards.
  Reply With Quote
Old January 18th, 2011, 07:59 AM   #4
tracer
Member
United States

tracer is offline
 
tracer's Avatar
 
Join Date: Nov 2003
Location: Near Dallas Tx
Posts: 63
Hello Harry: I don't have any exp with esa ts's. so can't help you with the specifics,
However I did Google "ESA Touchscreen" came up with numerous hits regarding cap screen failures, also found the esa company website. esa is one of those company's that require you to sign in. So you will have to goto the esa website and create an account, in order to download the manuals software etc.
  Reply With Quote
Old January 18th, 2011, 11:30 PM   #5
harrydeharry
Member
India

harrydeharry is offline
 
Join Date: May 2008
Location: Delhi
Posts: 237
Thank u Tracer,
I talked to the technical people of ESA and they told me the procedure of caliberation, after doing the caliberation touch screen starts working properly.
The procedure is just open the backplate of pannel, you will find a jumper there, remove the jumper from pin 2&3 and make in on pin 1&2.
Then power up the touch panel, a cailberation window will appear and follow the instructions.

Regards.
  Reply With Quote
Old August 23rd, 2012, 07:59 AM   #6
Sumedha
Member
Sri Lanka

Sumedha is offline
 
Join Date: Aug 2012
Location: Minuwangoda
Posts: 1
Quote:
Originally Posted by harrydeharry View Post
Thank u Tracer,
I talked to the technical people of ESA and they told me the procedure of caliberation, after doing the caliberation touch screen starts working properly.
The procedure is just open the backplate of pannel, you will find a jumper there, remove the jumper from pin 2&3 and make in on pin 1&2.
Then power up the touch panel, a cailberation window will appear and follow the instructions.

Regards.
Hi
I have faced the same problem with ESA VT505W. I opened the black plate, there is a jumper but haven't numbered it. just only 3 pins. So can you give more details
  Reply With Quote
Old August 20th, 2017, 10:36 PM   #7
jacklii
Member
China

jacklii is offline
 
Join Date: Aug 2017
Location: hong kong
Posts: 2
It's possible to control the button code doesn't completely overlap in the specified location, in general, is a hardware failure.
  Reply With Quote
Old August 24th, 2017, 05:48 AM   #8
jacklii
Member
China

jacklii is offline
 
Join Date: Aug 2017
Location: hong kong
Posts: 2
Here are hmi touch screen fault problem more detailed description https://nextion.itead.cc/2017/08/24/...ure-solutions/
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens TP270 no touch problem CarlosHo LIVE PLC Questions And Answers 2 April 21st, 2010 01:04 PM
Allen Bradley Panel View Plus 700 Touch Screen HMI Vipin LIVE PLC Questions And Answers 4 February 27th, 2010 03:58 PM
Siemens S7-314 MPI interface with Proface touch panel muthu_buddy LIVE PLC Questions And Answers 2 September 17th, 2009 02:17 AM
Easy view touch panel Fonzie66 LIVE PLC Questions And Answers 0 November 3rd, 2008 06:25 AM
Downloading a program to a touch panel Shohadawy LIVE PLC Questions And Answers 2 September 22nd, 2008 08:32 AM


All times are GMT -4. The time now is 09:04 PM.


.