connect to Panelview 600 with ethernet

bpoon

Member
Join Date
Apr 2006
Location
Olympia
Posts
7
Hi,

I am trying to download a Panelview application from my laptop to a Panelview 600 with a direction connection from the network card on my computer to the ethernet terminal on the Panelview.

Under the Communication Setup:
-DHCP is disabled
-IP address is 192.168.0.56
-Subnet mask is 255.255.255.0
-Interscan delay is 100ms

I have created an Ethernet/IP driver in RSLinx called 'panelview'
-IP address is 192.168.0.56
-Subnet mask is 255.255.255.0

I have also given my computer a static IP of 192.168.0.10.

The 'panelview' driver does not detect any device on the network. I am using a crossover cable to connect my computer to the Panelview. When I ping 192.168.0.56, everything looks fine.

This is the first time I've used a Panelview, so any help would be appreciated.

Thanks!

Ben
 
open rslinx classic
click on communications on pull down menu
click on configure drivers
single click on the ethernet driver you have already made.
(I use a normal TCP/IP ethernet driver for this, not the ethernetIP one)

click on configure.

add the ip address of the panelview in here.

you should then be able to see it then....
 
I've managed to connect and upload to the Panelview, but now I can't seem to get the Panelview to talk with my SLC 5/05 processor.


My Panelview has an IP of 192.168.0.56 and the IP of my SLC 5/05 is 192.168.0.100. My Panelbuilder application is set up to look for a network node with the IP address 192.168.0.100. I've connected the Panelview to the SLC 5/05 using a cross over cable.

Do I need to do something in the PLC program to recognize the Panelview terminal?

Thanks,

Ben
 
Both the panelview and SLC are demo's from a local distributor. No matter, though, I've got them talking now. Restarting the terminal fixed the problem.


Thanks,

Ben
 

Similar Topics

Hi. I am trying to connect PanelView 600, though RIO to the SLC500 DeviceNet card. I do not know if possible, but any help will bring me further...
Replies
13
Views
3,672
Client has multiple spare Panelview 550 (2711-T5A10 L1 PV550 Touch Devicenet)...
Replies
5
Views
643
can anyone help with trying to connect a panelview plus 7 to a pc i made a ip address for the panel view i ping it from my pc and its seeing it...
Replies
20
Views
3,383
I have a Brand new Panelview 800 2711R T7T A HMI that I can not connect to. Laptop IP address is 192.168.12.54 Static IP on HMi is 192.168.12.5...
Replies
19
Views
16,831
Hi, I hope everyone is well. I'm currently having a problem connecting to PanelView 1000 which was configured using PanelBuilder32 software. I...
Replies
1
Views
1,638
Back
Top Bottom