Hello,

Currently I am controlling the Powerflex 700H via Ethernet and everything is working well.

The client is wanting Auto/Manual function so when its on Auto the drive will control via PLC (ethernet) then when the drive is in manual, there will be Start and Stop push buttons that become available and this will control the drive to a fixed speed via digital inputs.

I am sure this will be possible I am just wondering if anyone out there has any experience in doing this?
 
Could you not simply wire the start/stop buttons as PLC inouts then do all your Auto/ Manual Control in 1 place??

I did a PF700 on Vector control that was hardwired to the PLC and all controlled via Ethernet/IP, this had start/stop control via the push buttons the fully auto control when required.
 
Last edited:

Similar Topics

Hi fellas, Hoping someone can help me get started with this. I'm a little out of my comfort zone trying to set up communication with a ProFace...
Replies
0
Views
789
Hi Group. We recently added a 20 COM E Module to our powerflex 700 and assigned IP parameters to it. It can pinged and verify the connectivity...
Replies
5
Views
2,479
I am programming an AB Compact Logix PLC (1769-L33ER) to control a PowerFlex 525-EENET VFD. I have the following questions: 1. I read on another...
Replies
9
Views
13,693
All, I am setting up some systems and am trying to utilize BOOL Inputs on my CompactLogix to trigger a change in frequency command on a PowerFlex...
Replies
5
Views
2,000
Going back to a 15 year-old project and upgrading the drives to PowerFlex 525. SLC 5/05 was controlling three non-AB drives with analog (for...
Replies
6
Views
9,388
Back
Top Bottom