Old December 12th, 2005, 10:46 PM   #31
darrenj
Member
Canada

darrenj is offline
 
Join Date: Feb 2005
Location: Ottawa
Posts: 1,003
Quote:
Originally Posted by Peter Nachtwey
Darrenj, yur pump still looks awfully big even if it supplies other tanks. Do you know the formula that relates power to flow and pressure?

Air activated valves will also add a lot of lag to the process. Have you considered an electric solenoid valve with LVDT feedback?

You can't P gain you way out of a PID problem. The P gain can only be increased so much. After a point the settling time can not be decreased. This limit on the effectiveness is dependent on the system.

Where is the trend? A trend is worth a lot more than 1000 words. It can save big $$$$.

Have you considered using a variable bias or feedforward?
Peter.. The pump mentioned (10HP) is only for the cleaning of tank..for the rest of the 20 odd hours it is a different pump that is programmed to supply the machine with 15PSI of milk..I am trying to set my system up on the worst case..I will know where i stand tommorow night..Hell this set up might not work..if not its back to the drawing board but i feel i should try every thing possible before i tell them its not going to work the way they want..
  Reply With Quote
Old December 12th, 2005, 10:47 PM   #32
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 10,002
Darren,

I think that you have mixed up the TWO different methods that I have mentioned here. In the second method, you read in a new pressure every 1 second, or whatever time period that you think is needed for accurate control. Take the old average and multiply it by 3. Take this number and add it to the new pressure reading. Divide the total by four and save this as the new average reading.

Average = ((3 x Old Average)+ new reading) / 4

You can use a different multiplier and divisor other than 3 and 4 (for example, 4 and 5). I used 3 & 4 because I found that I can usually make this work with only 16-bit integer numbers, and some PLCs only have 16-bit integers.

Last edited by Lancie1; December 12th, 2005 at 10:52 PM.
  Reply With Quote
Old December 12th, 2005, 10:49 PM   #33
darrenj
Member
Canada

darrenj is offline
 
Join Date: Feb 2005
Location: Ottawa
Posts: 1,003
o.k. that makes more scence to me now..!!
  Reply With Quote
Old December 13th, 2005, 02:57 PM   #34
parky
Member
United Kingdom

parky is offline
 
Join Date: Oct 2004
Location: Midlands
Posts: 979
Even with the problem of the foaming, it would be simpler to use the analog output to set a pre-determined speed based on the following.

if one pump is running, pre-set the analog output to give a flow a little above the flow of the delivery pump or pumps running, then if 2 set another flowrate etc.
i.e. 3 presets for combination of the pumps pumping out the liquid & another for CIP.
I agree about the average method of sampling the analog pressure transducer, then again it would have been cheaper to use 3 level probes (although not if the medium is like oil that would require capacitive probes).
Simple is often the best!.
  Reply With Quote
Old December 14th, 2005, 02:47 AM   #35
darrenj
Member
Canada

darrenj is offline
 
Join Date: Feb 2005
Location: Ottawa
Posts: 1,003
Well i got it figured out.. I think Ken was the closest to guessing the problem..I should have figured it out as soon as i saw the -14 reading..When the tank started to overflow and i entered a smaller number to close the valve..the valve closed..HOWEVER The overflow line was full of liquid and tried to drain..This caused suction in the tank giving me a negative reading..(Dont forget the pressure sensor is only 0-1psi)..Once i figured that out it was only a case of programming the drain valve to open for a second or 2 to break the suction and everything was good..

I got the PID working o.k. but not great..But that will take some time changing values and seeing what works best..

Thanks all for the help..

Lance1 the average worked great, but caused a bit of a lag in the PID..I tried it without and seems to work good now that i have the overflow sorted..

Now i just have to adjust the program to work ith the new sensor..

One more quick question.. The operator can close the inlet valve by the HMI. When he does this i want the Output from the PID to go to 0 Can i write a 0 to the CV to force it off??

Thanks
D
  Reply With Quote
Old December 14th, 2005, 02:55 AM   #36
CroCop
Member
United States

CroCop is offline
 
Join Date: Aug 2005
Location: Utah
Posts: 1,050
Why don't you write the CV to a float, and pass a 0 to that float when you need the output off?

As well as shut off the PID loop so you don't build wind up a very large integral.
  Reply With Quote
Old December 14th, 2005, 02:57 AM   #37
darrenj
Member
Canada

darrenj is offline
 
Join Date: Feb 2005
Location: Ottawa
Posts: 1,003
Quote:
Originally Posted by CroCop
Why don't you write the CV to a float, and pass a 0 to that float when you need the output off?

As well as shut off the PID loop so you don't build wind up a very large integral.
Good point..why dont i do that!!

Sometimes you just look right over things..

Cheers
D
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PID for MicroLogix 1500 - conversion issues ... Ron Beaufort LIVE PLC Questions And Answers 5 November 8th, 2005 10:03 AM
learning PID for Allen-Bradley ... Ron Beaufort LIVE PLC Questions And Answers 9 August 23rd, 2005 02:40 PM
AB PLC5 PIDs Derek McFarland LIVE PLC Questions And Answers 23 March 2nd, 2005 02:18 AM
Use a PID? MarBa LIVE PLC Questions And Answers 4 May 8th, 2003 09:31 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 11:57 AM


All times are GMT -5. The time now is 10:36 AM.


.