Member
|
Siemens TIA Portal V13 and Safety System V2.1
I am working on a program that was developed in 2015 for an S7-300 safety PLC. The new copy of this machine uses an S7-1500 safety plc. We were asked to stay at Portal V13 if we could.
The F-IO DBs in the S7-300 included point specific quality (status) inputs (QBAD). This didn't come in with the S7-1500 until safety system 2.1. My development library currently only lets me go as high as safety system V1.3. I would like to use the point specific QBAD bits if possible since that is how the previous program was written. Is safety system 2.1 compatible with Portal 13 as an update or would I need to go to a higher version of Portal to get safety system 2.1? Thanks, Keith |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,910
|
According to this document, it looks like you need V14 or higher. If you obtain a V18 license, you can run older versions under it.
https://cache.industry.siemens.com/d...1C_A1_1.20.pdf
__________________
Automation Programmer PLC / HMI / SCADA / SQL New Systems, Modifications System Upgrades & Conversions Siemens EPROM & EEPROM Service ------------------------ Visit: contrologica.com Email: info@contrologica.com Last edited by sigmadelta; March 18th, 2023 at 05:42 PM. |
![]() |
![]() |
#3 |
Member
|
Understood. Thank you.
Keith |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Aug 2021
Location: UK
Posts: 2
|
Unfortunately, it is not possible to update the Portal V13 to Safety System 2.1. The latest version of the Portal software compatible with Safety System 2.1 is V14 Update 3. Upgrading to this version will be necessary if you would like to use the point specific QBAD bits in the S7-1500 safety PLC.
|
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Feb 2006
Location: Central Wisconsin
Posts: 160
|
The Safety System 2.1 is also hardware specific. So even if you upgrade to the latest version of TIA Portal you may not get point specific QBAD from all your hardware.
TIA Portal V13 was unstable in my opinion; 15.1 was really the first version that was fairly stable. Also 1500 CPU's should be at or above firmware 2.8 so they are stable. I believe V14 only supports up to firmware 2.1 of the 1500. |
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
Since you cannot stay at V13, if you must upgrade versions, why not go to the latest and greatest?
__________________
Certified Siemens Functional Safety Professional, ID: SFSP17010238 NRA Benefactor |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
TIA Portal hardware catalog in relation to F-DI / F-DO modules | kobelu_090 | LIVE PLC Questions And Answers | 8 | July 27th, 2015 11:38 AM |