UL standards for a panel in a C1D2 location

Hello folks. I have a panel project that, as I understand it, will require UL labeling, and the more I look into UL standards, the more I think that I am in over my head (not with the panel itself, but with the UL label).

The project is a Z-purged NEMA 4X stainless panel with a PanelView Plus 7 Performance HMI mounted in the door. The panel will be mounted on the equipment, which will be installed in a Class 1 Div 2 location...in California.

From what I have read, California has very strict regulations governing electrical installations, one of which is approval by a NRTL. I started looking into UL approval and found that if all my ducks are in a row, I can have a UL certified panel shop inspect the panel and apply their label to it. My problem is finding a panel shop with the correct certification. I have been unable to even find which UL standard applies in this situation. UL698A seems to govern only panels installed in a safe location that have intrinsically safe circuits extending into a hazardous location. In the case of my current project, the panel will be installed within the hazardous location.

At this point, I just need to know what UL standard(s) governs this project. Can anyone point me in the right direction?
__________________
here comes the time when people will behave like madmen, and if they see anyone who does not behave this way, they will rebel against him, saying "you are mad" because he is not like them. - st. anthony the great
  Reply With Quote
Old January 10th, 2018, 04:41 PM   #2
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,530
I am pretty sure you will be looking for a shop that has NNNY certifications. There is also NRBX that covers panels in Explosive areas. I used to have these certifications too but have sense moved on.

You can also call UL and have a Field Inspection done on your panel. A UL Inspector will come out and if everything meets the standard he will put a UL label on the panel.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old January 15th, 2018, 01:17 PM   #3
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,466
UL listed panels are governed by UL508A.
You cannot build this panel and get it certified by a ul shop unless the rules have changed. to become a ul panel shop requires a lot of paperwork.
there are lot's of details involved in building a ul listed panel, I would try to find one. I know of a ul panel shop in West Tennessee if it helps, I haven't been in contact with them in several years.

the next problem that I see is you have the panelview terminal in a z purged panel, the terminal is not rated for a zpurge system, the display can break. Check with AB to see if the ratings have changed in the last 6 years.

regards,
james
  Reply With Quote
Old January 15th, 2018, 02:19 PM   #4
isiah_s
Member
United States

isiah_s is offline
 
Join Date: Sep 2016
Location: NYC metro
Posts: 45
You can not do it yourself you need someone certified.

UL-508A
NFPA 70

Each part in the panel needs to be UL as well. Just a quick question about your purge system: is the gas heavier or lighter than air? This effects how it should be mounted.
  Reply With Quote
Old January 15th, 2018, 04:42 PM   #5
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,124
I would suggest hiring a panel shop in California, there are a few other idiosyncrasies that exist out here, local panel shops know them all. There are shops that will just build the panel to your design and let you take care of all the programming etc. Northern or Southern CA?
  Reply With Quote
Old January 22nd, 2018, 07:45 PM   #6
kchap
Member
United States

kchap is offline
 
Join Date: Nov 2011
Location: Peculiar, MO
Posts: 9
Quote:
Originally Posted by jraef View Post
I would suggest hiring a panel shop in California, there are a few other idiosyncrasies that exist out here, local panel shops know them all. There are shops that will just build the panel to your design and let you take care of all the programming etc. Northern or Southern CA?
It will be going to the bay area. I am chest deep in the project at this point, so it is too late to have another shop do it. It is a simple panel, so hopefully it should not be TOO big of an ordeal. That said, any heads-up on California's idiosyncrasies would be most welcomed!

I found the information I was looking for in regard to which UL standard applies (NNNY in this case). I have opted for a field evaluation, and I also have 508A and 698A certs on my radar screen.
__________________
here comes the time when people will behave like madmen, and if they see anyone who does not behave this way, they will rebel against him, saying "you are mad" because he is not like them. - st. anthony the great
  Reply With Quote
Old January 22nd, 2018, 08:00 PM   #7
kchap
Member
United States

kchap is offline
 
Join Date: Nov 2011
Location: Peculiar, MO
Posts: 9
Quote:
Originally Posted by James Mcquade View Post
the next problem that I see is you have the panelview terminal in a z purged panel, the terminal is not rated for a zpurge system, the display can break. Check with AB to see if the ratings have changed in the last 6 years.

regards,
james
That has long been a point of debate. To my knowledge, there is no rating that applies to a HMI mounted in a purged/pressurized enclosure (aside from a HazLoc rating). Rockwell advises against it, but I think that is more of a CYA kind of thing, because as you said, the screens can bulge and break. However I suspect that would be due to over-pressurization. There are quite a few being used in this kind of application where I work, and no one in our EE group has ever had a problem with them.
__________________
here comes the time when people will behave like madmen, and if they see anyone who does not behave this way, they will rebel against him, saying "you are mad" because he is not like them. - st. anthony the great
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Australian Control Panel Standards RBergmann LIVE PLC Questions And Answers 10 January 19th, 2014 01:04 PM
OT- Wiring of mcb in a panel cjd1965 LIVE PLC Questions And Answers 44 April 15th, 2013 05:24 PM
UL Control Panel Required? Bteachman LIVE PLC Questions And Answers 1 November 10th, 2009 11:57 PM
Exhaust inside hazardous location panel DaveW LIVE PLC Questions And Answers 2 November 30th, 2005 01:22 PM
UL Listed panel shop RDay LIVE PLC Questions And Answers 5 January 11th, 2004 07:59 PM


All times are GMT -4. The time now is 02:40 PM.


.