Posts: 8
|
Omron NX remote IO
Hey yall,
I have a project where I am using an NX EIC202 remote IO unit and an NX102 PLC. The problem I am having is that the IO is on a different network than the PLC in the facility and I cant get them to communicate. Have any of you had any experience getting things like this to talk across the different networks? |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
Why are they on different networks?
For deterministic IO, that is just wrong. If they must be on different networks, you would be better off putting another PLC on the other network & messaging. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Aug 2009
Location: alabama
Posts: 8
|
That’s the network setup at the facility. Putting in another PLC isn’t really an option.
|
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2015
Location: Yokohama
Posts: 1,285
|
prodigy, hi. I do not get the requirement clearly.
The NX102 PLC is an EtherNet/IP scanner and the NX EIC202 is an EtherNet/IP adapter and they are in physically separate networks? How is the physical connection established? By means of a router? Is there a requirement to establish IO communication between the PLC and the remote IO, or would periodical explicit message request from the PLC to the remote IO suffice? I think the requirements need to be refined, or we cannot provide useful advice. |
![]() |
![]() |
#5 |
Lifetime Supporting Member
|
What can I say - stupid! LOL IT driven I guess.
__________________
The Old Pfhaart ![]() |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Aug 2009
Location: alabama
Posts: 8
|
Yes, they are connected to different network switches in the plant. For example, the IO would be on a 12.232.42.xxx and the PLC would be on a 12.232.45.xxx network. I only need to turn on 3 outputs from time to time to turn on a a set of lights.
|
![]() |
![]() |
#7 |
Lifetime Supporting Member
|
Then you might get away with changing the 3rd octet of the subnet mask, assuming it's currently /24.
Sounds like IT created the problem, throw it back at them.
__________________
Regards, Patrick G. B.Eng MIET Making the flashy lights flash since the 90's SCADA - Inductive Automation Gold Integrator | PLC | Control Panels | Robotics | Training Connect with Matrix Engineering My son was chewing on an electrical cord, so I had to ground him. He is doing better currently and conducting himself properly. My electrical skills are quite poor, which is a shock to some people ![]() |
![]() |
![]() |
#8 |
Lifetime Supporting Member
|
Have you set the gateways correct at each end?
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Allen Bradley 1734-AENT/A remote IO | drewster | LIVE PLC Questions And Answers | 2 | November 17th, 2017 12:28 PM |
Omron CX Programmer Remote IO Monitoring | Steve_D | LIVE PLC Questions And Answers | 4 | January 19th, 2017 07:43 AM |
adding new AI to PLC5 as remote IO | FASEELATH | LIVE PLC Questions And Answers | 6 | March 31st, 2011 09:45 AM |
Omron Ethernet/IP to AB Point IO | AndrewY | LIVE PLC Questions And Answers | 1 | August 26th, 2009 08:17 AM |
Beckhoff Remote IO and Unitronics V280 | TimothyMoulder | LIVE PLC Questions And Answers | 2 | May 24th, 2005 12:11 PM |