Old December 6th, 2010, 09:44 AM   #1
James Fillmore
Lifetime Supporting Member
United States

James Fillmore is offline
 
Join Date: Sep 2004
Location: Detroit, MI
Posts: 45
Question Power drops to control panel question...

We are building a line of standardized machines; servo driven press, high power IR lamp, plastic assembly machines. A stand alone machine.

I'm thinking of creating a servo / plc enclosure and then a power enclosure. Reason is the servo / plc panel would be very standard but the power panel could be anything from a few kw of phase angle power control to hundreds of kw.

The plc / servo panel would require about 30A of 480VAC. The IR power panel would require 60A to over 600A of 480VAC. Out of convenience for the customer it'd be nice to have one 480VAC drop and then quick connect the PLC panel to the IR power panel. Only connections between the 2 would be 480VAC power for the servo equipment and power supplies. And a couple dozen digital and analog control wires from the PLC to the power controllers and contactors.

Bottomline, SHOULD I have (2) 480VAC power drops? If I did the only wiring between the 2 control panels would be low voltage.

If I had (1) drop on the IR power panel I'd have to run 480V to the plc / servo panel. Would probably have to feed the top of a disconnect on the plc / servo panel. Would be nice if this was or could be made a quick disconnect cable to the IR power panel.

Anyone done something similar? Any suggestions?

TIA
  Reply With Quote
Old December 6th, 2010, 03:30 PM   #2
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,152
Its done all the time. We do something similar on our large hydraulic presses. We run the main 480V drop to one panel. In that panel we route through a smaller breaker, then take 480V to the second panel. The second panel also has a disconnect/breaker.

Since your power is leaving the first cabinet make sure you use a breaker rated for branch circuit protection and not a supplemental protection breaker. Because its 480V, plan on a disconnect and door interlock at the second panel as well as the first.

It goes without saying, adhere to NEC rules.
__________________
True craftsmanship is only one more power tool away.

That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
  Reply With Quote
Old December 6th, 2010, 03:44 PM   #3
James Fillmore
Lifetime Supporting Member
United States

James Fillmore is offline
 
Join Date: Sep 2004
Location: Detroit, MI
Posts: 45
Do you hard pipe/wire the 2 together or quick disconnect them?

Do you just label "power fed from another source" or something or do you use yellow or yellow striped black wire to run the 480V from the power panel to the PLC panel?

Yep, I'd have a small disconnect on the plc / servo panel.

Thanks for the info!
  Reply With Quote
Old December 6th, 2010, 04:08 PM   #4
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,124
For only 30A I would do it with multi-pin connectors. I like Brad Harrison / Woodhead (now part of Molex). They have a power connector called Brad Power and then use the regular Brad/Woodhead Minichange connectors for the control circuits. You can key the control connectors so that they cannot be plugged in the wrong sockets.
  Reply With Quote
Old December 6th, 2010, 04:14 PM   #5
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,152
We hard pipe them together. The panels are labeled for power source. Also the second panel disconnect is labeled to indicate that it only shuts off a portion of the machinery.
__________________
True craftsmanship is only one more power tool away.

That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
  Reply With Quote
Old December 6th, 2010, 08:31 PM   #6
nwboson
Member
United States

nwboson is offline
 
nwboson's Avatar
 
Join Date: Mar 2009
Location: Portland, Oregon
Posts: 233
I'm in the same camp as Alaric: you can't beat hard wiring for reliability.

Don't forget to think about your neutral conductors, earthing requirements, and how you're going to avoid any ground loops.

It is common practice to run all your power into one panel then distribute out from there with separately fused (breakered) branch circuits. This also gives you the opportunity to properly label your FLA for your entire system.

Do your earthing in just that one panel, run your current carrying neutrals so they all only get their earth reference at only that one location. Ground loops can make your PLC circuits a nightmare!
  Reply With Quote
Old January 16th, 2011, 09:20 AM   #7
tracer
Member
United States

tracer is offline
 
tracer's Avatar
 
Join Date: Nov 2003
Location: Near Dallas Tx
Posts: 63
with all the arc flash stuff, it's becoming more common to have your high voltage in one cabinet, and the plc and low voltge components in another...
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Control Panel Pics kbcombs LIVE PLC Questions And Answers 3 November 17th, 2005 11:43 AM
Lightning Protection for Control Panel?? anks LIVE PLC Questions And Answers 5 November 6th, 2005 12:30 AM
Control panel transformer sizing pauly LIVE PLC Questions And Answers 7 April 19th, 2005 09:14 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 11:57 AM
Panel View & Control Logix gizmo LIVE PLC Questions And Answers 8 September 21st, 2002 10:52 PM


All times are GMT -4. The time now is 01:38 PM.


.