Yo, Craig,
Well, Allen beat me at typing - as usual - but here's my $0.02 anyway -
The short answer to your question is "yes".
If you set "Limit Output CV" to YES, then the Integral term will "freeze" at its current value whenever the CV gets up to the value you have entered for "Output Max CV%". The Integral term will also "freeze" at its current value whenever the CV drops as low as the value you have entered for "Output Min CV%".
If you leave "Limit Output CV" set to NO, then the Integral term will "freeze" at its current value whenever the CV gets up to 100% - or if the CV drops to 0%. In other words, if the "Limit Output CV" is set to NO, then the values for "Output Max CV%" and "Output Min CV%" will have no effect on the Integral term - but the Integral will still be "automatically" limited when the CV gets to 0% or 100%.
When most programmers use this "Limit Output CV" feature they aren't really thinking about its effect on the Integral term. Usually they are just interested in limiting the CV to a specific range of values. Examples: Don't let the CV go too low - we need an idle setting. Or don't let the CV go too high - there's NO WAY we'll ever want THAT much gas.
I'm just curious but are you having an issue with Integral wind up - or just digging a little deeper than most people do? Keep in mind that if you DO use this feature (to prevent the Integral term from "winding up") then you are also (unintentionally?) limiting the CV to values between the "Output Max CV%" and "Output Min CV%" settings. Is that something that you really want to do?
Finally, if you want to experiment with these features, monitor words 17 and 18 in your PID control block area. That's where the Integral term is stored. You can actually watch it increase, decrease, and "freeze" as you manually manipulate the parameters of a "dummy" PID control. You'll learn a lot more this way than by trying to figure out what the book means. Been there - done that.