PID & Panel View 1000

plcnovel

Member
Join Date
Feb 2006
Location
LHR
Posts
215
Hi Everybody
I am trying to use a couple of pid loops in my system (slc 5/4, panel view 1000). For derivate term or the rate term in the PID controller, how can i input on the PV screen a value less than 1, or a decimal value that can actually be used in the pid equation? Like rate derivative term is a integer file address in the controller, so even i be able to add a decimal value in the PV screen, it would be rounded off to an intger......so First, how can i enter a decimal value in the rate input field on the PV screen (do i have to change the formatting of my data entry label on the screen)? and SECONDLY, how would i be able to use that decimal value in the controller? DO i have to use some kind of scaling and offset, if yes if you can explain to me wth some example how to do that , it would really be much appreciated? Thanks in advance?
 
See Attached PDF:

Word 5 is the Rate term, the integer value you enter is
multiplied internally by .01 (ie. if you enter 50 the Rate
term would be .5) Hope this helps
 

Similar Topics

Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
70
Hello, I have a motor that we are sending a RPM Speed Output from 0-100% to the VFD. However, the Motor HP needs to be limited to 6000 HP and the...
Replies
3
Views
88
I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
Replies
13
Views
600
Hi all, I'm having trouble solving a problem I've been working on for several months, and thought you might like a stab at it. The machine runs...
Replies
22
Views
947
How can I connect PID Output to a valve. In ladder logic program is there any logic do I want to add between valve and PID? PV=SP What will be the...
Replies
7
Views
413
Back
Top Bottom