Originally Posted by Bit_Bucket_07 View Post
Sounds to me like you're getting EMF from a variable speed drive. That could be because your transducer (or transducer wiring) is too close to the motor or the cable feeding the motor. I've even seen noise introduced into the AC control power from drives without input reactors or an isolation transformer affect analog inputs. Is your instrument cable run inside a steel conduit? A shield can only reject so much noise.
currently the wires are only connected from the control cabinet to the machine for testing purposes within the shop, so they are in no conduit at all. although the is quite close to a slew of high voltage AC wire, i will have to rectify that tomorrow.

-are analog output signals just as susceptible to noise? i have an analog output card in the cabinet sending two separate 4-20ma signals to two separate vfds for speed control and watching the drives the HZ stays dead nuts when commanded.

-could i test with a voltmeter how much noise i am seeing on the signal wire? lift the shield from the cabinet, put it on one probe on meter, put other probe on meter to ground? or would i lift the signal wire from the transducer and use that while leaving the shield in place?
  Reply With Quote
Old May 17th, 2018, 09:13 PM   #32
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,401
Quote:
Originally Posted by JZerb View Post
-are analog output signals just as susceptible to noise?
Yes.


Quote:
Originally Posted by JZerb View Post
-could i test with a voltmeter how much noise i am seeing on the signal wire? lift the shield from the cabinet, put it on one probe on meter, put other probe on meter to ground? or would i lift the signal wire from the transducer and use that while leaving the shield in place?
I'm assuming that you can see the effect of the noise on your analog input. An oscilloscope would be the ideal instrument for monitoring EMF levels, but you should be able to identify and correct the problem without using a scope.

Moving your signal wiring away from any AC power wiring is a good first step.
__________________
  Reply With Quote
Old May 17th, 2018, 09:28 PM   #33
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 167
Quote:
Originally Posted by Bit_Bucket_07 View Post
Yes.




I'm assuming that you can see the effect of the noise on your analog input. An oscilloscope would be the ideal instrument for monitoring EMF levels, but you should be able to identify and correct the problem without using a scope.

Moving your signal wiring away from any AC power wiring is a good first step.
My plan to solve the problem tomorrow is to first move the wiring. Second, then possibly get the transducer manufacturer on the phone and see if they recommend the unit being mounted to metal to act as a ground for the case, or if it can be installed as it currently is with the plastic ďisolatorĒ between it and the metal.
  Reply With Quote
Old May 18th, 2018, 03:08 AM   #34
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,245
Instead of regular terminals for the shield, use dedicated shield terminals. See post #12.

The other thing you can do is to fight the noise at the source.
Do the VFD have an output filter ?
Are the motor cables shielded ? The shielded motor cable can be grounded in both ends (signal cables only one end).

edit: The isolator between transducer and machine mount could have something to do with avoiding ground loops.
IMO it would be a design flaw if the electronics inside transducer is not already isolated from the transducer housing. But may it is not isoloated, hence the need for the isolator.
__________________
Jesper
3 strikes and you're out

Last edited by JesperMP; May 18th, 2018 at 03:11 AM.
  Reply With Quote
Old May 18th, 2018, 04:22 AM   #35
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 167
Quote:
Originally Posted by JesperMP View Post
Instead of regular terminals for the shield, use dedicated shield terminals. See post #12.
Iím new to all of this, control panel design and building even more so then programming and such. Are those just ground buss bars in that picture? Iíve never seen anything that neat in my searching for buss bars on the companies websites that we typically deal with.


Quote:
Originally Posted by JesperMP View Post
The other thing you can do is to fight the noise at the source.
Do the VFD have an output filter ?
Are the motor cables shielded ? The shielded motor cable can be grounded in both ends (signal cables only one end).
Iím not sure, I would assume it does I will look today.
The motor cables, against my request, are not shielded.

Quote:
Originally Posted by JesperMP View Post
edit: The isolator between transducer and machine mount could have something to do with avoiding ground loops.
IMO it would be a design flaw if the electronics inside transducer is not already isolated from the transducer housing. But may it is not isoloated, hence the need for the isolator.
I agree. But it was interesting to me to read one manufactures install instruction which specifically states to make sure the body is bolted to a grounded metal surface, and then the manufacturer that we use says no such thing one way or the other.
  Reply With Quote
Old May 18th, 2018, 08:25 AM   #36
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,245
Quote:
Originally Posted by JZerb View Post
Are those just ground buss bars in that picture?
Yes. With specifically the purpose to terminate the shields. The difference is that with the clamp the shield has a much better connection to ground, as compared to twisting it together and sticking it in a regular terminal.

Quote:
Originally Posted by JZerb View Post
[..]one manufactures install instruction which specifically states to make sure the body is bolted to a grounded metal surface,
That one probably has isolated electronics. Grounding the housing will work the same as grounding the shield. But.... if the housing is grounded, then make sure the shield is only grounded at that end, and not at the other end.
Or (!) .. make sure the shield is not connected to the housing, and then ground the shield at the other end.
Both to avoid current loops.

Quote:
Originally Posted by JZerb View Post
[..] and then the manufacturer that we use says no such thing one way or the other.
Then in that one the electronics is probably not isolated.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old May 18th, 2018, 07:46 PM   #37
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 167
I moved the signal wire away from the high voltage ac wires from when we just interconnected the machine to the control panel for in house testing purposes and that seemed to clean up the noise a bit.

It’s still an issue in as much as when the motor is running that’s moving the object that the transducer is attached to, you get a reading that’s about 2inches off from actual once said motor stops it’s output.

I liffed the shield wire and attached my meter to it, and the other side of the meter to ground. There is AC mV worth of noise on the drain wire, ranging from 60-160mV depending on which motors are running. So I assume that’s still my issue with my less then ideal 4-20ma reading into my PLC.

I will look into building my next machine cabinet where I require 4-20ma signals with the ground buss bar for shields as mentioned above to hopefully quell some if not all of th me issue I’m having now.
  Reply With Quote
Old May 18th, 2018, 09:39 PM   #38
milldrone
Member
United States

milldrone is offline
 
milldrone's Avatar
 
Join Date: Mar 2005
Location: in the dog house
Posts: 1,292
I would like to suggest some tests to help you determine the source of your problem.
1. When you move in both directions does the measurement always "jump ahead" (2 inches in the direction you are traveling) when you stop?
2. Presuming the VFD is moving the item you are measuring can you disconnect the motor from the movement or disconnect the analog sensor from the item. Then run the VFD and note any changes in the analog sensor reading.
3. Finally move the sensor as close to speed as you can by hand and note the readout. Try this with the VFD running and not running.
4. Again presuming the VFD is moving the sensor. Run the VFD as slow as you can and note the sensor error.
__________________
Vaughn

If you can read this, thank a teacher.

Last edited by milldrone; May 18th, 2018 at 09:45 PM.
  Reply With Quote
Old May 19th, 2018, 05:46 AM   #39
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 167
Quote:
Originally Posted by milldrone View Post
I would like to suggest some tests to help you determine the source of your problem.
1. When you move in both directions does the measurement always "jump ahead" (2 inches in the direction you are traveling) when you stop?
2. Presuming the VFD is moving the item you are measuring can you disconnect the motor from the movement or disconnect the analog sensor from the item. Then run the VFD and note any changes in the analog sensor reading.
3. Finally move the sensor as close to speed as you can by hand and note the readout. Try this with the VFD running and not running.
4. Again presuming the VFD is moving the sensor. Run the VFD as slow as you can and note the sensor error.

1. Iím 99.9 percent sure that is the case, I will double check Monday morning.
2. A VFD is moving the item that the string transducer is attached to yes. I can easily disconnect the analog sensor from the movement and then run the machine and see what noise comes into the analog card.
3. I can do this as well Monday morning.
4. The vfd currently runs at two different preset frequencies, 10 and 40hz, I can lower the lesser frequency and see what I get

Thank you for the ideas!
  Reply With Quote
Old May 21st, 2018, 05:33 PM   #40
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 167
Quote:
Originally Posted by milldrone View Post
I would like to suggest some tests to help you determine the source of your problem.
1. When you move in both directions does the measurement always "jump ahead" (2 inches in the direction you are traveling) when you stop?
exactly

Quote:
Originally Posted by milldrone View Post
2. Presuming the VFD is moving the item you are measuring can you disconnect the motor from the movement or disconnect the analog sensor from the item. Then run the VFD and note any changes in the analog sensor reading.
there is the same amount of noise it seems. sadly dont have a scope to be absolutely sure.

Quote:
Originally Posted by milldrone View Post
3. Finally move the sensor as close to speed as you can by hand and note the readout. Try this with the VFD running and not running.
moved the sensor with the vfd by hand and it still read the same. i did also just move the sensor itself, without the vfd on and once i stopped the reading stopped dead on.

Quote:
Originally Posted by milldrone View Post
4. Again presuming the VFD is moving the sensor. Run the VFD as slow as you can and note the sensor error.
when i run less HZ from the VFD the noise is absolutely less.

i pulled the cabling that runs to the transducer out of the machine to get clear and away from any high voltage AC wire, cleaned up the signal a bit but still not good enough.
  Reply With Quote
Old May 21st, 2018, 08:07 PM   #41
milldrone
Member
United States

milldrone is offline
 
milldrone's Avatar
 
Join Date: Mar 2005
Location: in the dog house
Posts: 1,292
Quote:
Originally Posted by JZerb View Post
moved the sensor with the vfd by hand and it still read the same. i did also just move the sensor itself, without the vfd on and once i stopped the reading stopped dead on.
Well, that narrows it down to the VFD as the culprit (not that it was a surprise)

Quote:
Originally Posted by JZerb View Post
i pulled the cabling that runs to the transducer out of the machine to get clear and away from any high voltage AC wire, cleaned up the signal a bit but still not good enough.
If I remember correctly you requested shielded cables for the motor and you were denied. If your application needs a flexible power connection to the motor you will need (barring shielded cable) liquidtite and grounding lead from the motor to the drive, then to the ground buss.

Another preventive measure would be a signal conditioner/isolator
https://www.eurotherm.com/products/i...ction-iq-ac-dc
https://www.automationdirect.com/adc...er_Input/FC-11
__________________
Vaughn

If you can read this, thank a teacher.
  Reply With Quote
Old May 21st, 2018, 09:42 PM   #42
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 167
can you actually SEE the noise with an oscilloscope? i know you can use one to see noise on an encoder, but since this transducer puts out a 4-20ma signal and not just pulses like an encoder would can a scope still be a useful tool? how would one determine if the 24v signal could be "dirty", i assume that youre thinking that could be an issue since you recommended a signal conditioner for said instrument.

Quote:
Originally Posted by milldrone View Post
If I remember correctly you requested shielded cables for the motor and you were denied. If your application needs a flexible power connection to the motor you will need (barring shielded cable) liquidtite and grounding lead from the motor to the drive, then to the ground buss
correct, was told that "its not needed"
there are 4 separate motors on this machine, all needing flexible power connections. i assume with the liquatite you would want me to run it from the motor to the junction box on the machine...junction box on machine to the main cabinet will be liquatite or conduit once installed on site. issue with the former is at this point that not possible, would need to do that earlier on in the machine build.


Quote:
Originally Posted by milldrone View Post
this i will order tomorrow from auto direct and see if that does the trick. ideally next machine i will be more convincing and get shielded motor cable in there to quell any of these issues before they become issues. Thanks all for the recommendations.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Shielded Wire Duct The Plc Kid LIVE PLC Questions And Answers 2 December 1st, 2011 11:00 AM
AWG wire sizes in the European Union TConnolly LIVE PLC Questions And Answers 4 September 20th, 2010 07:57 PM
Proper way to wire overloads Maintenance Man LIVE PLC Questions And Answers 26 November 29th, 2009 08:31 PM
Wire flexability for data collector rpoet LIVE PLC Questions And Answers 3 August 12th, 2008 10:26 PM
Do I need a shielded wire for 4-20mA signal? Cryogen LIVE PLC Questions And Answers 6 March 17th, 2006 08:24 AM


All times are GMT -5. The time now is 09:54 PM.


.