I have a FX3U48M Delema

OK I have FX3U48 MR/ES-A And it seems to stop giving the signal Threw Y7 to start the belt to take the product to another conveyor. The Y7 on the bottom of the PLC connects to the bottom of the 24V relay coil and the top of the coil is connected to the 24V+ of the FX2N 16 EX controller.



The only way I can get the belts to move is if I jumped a wire from the -24V of the converter to the bottom of the relay which makes the belts run all the time. I tried a new PLC New relay replaced the photo sensors tried to reenter the program in to the PLC from another since they are all programmed and wired up the same and nothing seems to work I even ran new cables from the main box to the belts and nothing seems to fix this problem.




Any suggestions?
  Reply With Quote
Old August 17th, 2018, 10:46 AM   #2
nehpets
Member
Wales

nehpets is offline
 
nehpets's Avatar
 
Join Date: Mar 2009
Location: Wales
Posts: 354
I know it sounds a bit obvious but have you connected the S/S terminal?


Steve
__________________
Why do programmers get confused between Halloween and Christmas - OCT31 = DEC25
  Reply With Quote
Old August 17th, 2018, 11:04 AM   #3
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
Hmm
  Reply With Quote
Old August 17th, 2018, 11:35 AM   #4
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
Yes yes it is 24V
  Reply With Quote
Old August 18th, 2018, 12:39 AM   #5
goghie
Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 236
Just to make clear. Fx2N-16EX is not controller, it is digital input card and it's S/S signal should be connected to +24V or -24V depending what do you want - sink or source input. By your information it's connected to +24V so it is sinked, meaning that by applying 0VDC to FX2N input will give to PLC program signal that the mentioned relay contact is opened or closed depending how it is wired. Did you checked relay wiring?
Does it's LED changes the state when you apply voltage to relay's coil?
On other side FX3U-48MR/ES ist PLC and it has rela outputs, so it should be very easy to check does it has faulty output. Is it Y7 output (as you wrote) LED on? When the LED is on you can try is the output also working...
But in reality it is hard to troubleshoot without application and PLC connected to PC.
  Reply With Quote
Old August 18th, 2018, 05:22 AM   #6
Mad_Poet
Member
United States

Mad_Poet is offline
 
Join Date: Feb 2017
Location: Virginia
Posts: 227
I would say check that the inputs light up the appropriate LED's on the PLC. Then get into the program in 'monitor mode' (so that you can 'see' that the inputs are making it into the PLC program). Verify that the inputs come and go as they ought. Then locate the rung with the output Y7 and see which relay contacts are not closing to activate it. You should also be able to 'force' contacts in the program to turn them on and verify if the PLC can really actuate the output and drive the motor.
Poet.
  Reply With Quote
Old August 18th, 2018, 06:36 AM   #7
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
Y7 is lit up on the PLC but nothing happens. Will check with the program the bad thing is there are no comments anywhere only like Y007 and X001 so I have to spend time tracking down sensors and other stuff lol.
Attached Images
File Type: jpg 20180818_054943.jpg (187.8 KB, 81 views)
  Reply With Quote
Old August 18th, 2018, 06:59 AM   #8
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 884
Good Lord. That panel fills me with horror.
  Reply With Quote
Old August 18th, 2018, 07:01 AM   #9
Mad_Poet
Member
United States

Mad_Poet is offline
 
Join Date: Feb 2017
Location: Virginia
Posts: 227
Hmmmm.
Y7 output is lit but nothing happens.
Is there 24 volts across the relay coil?

The Y7 output . . is it supposed to be providing + 24 Vdc?
Or is it supposed to provide a ground to the coil?
Is Y7 a relay output? If so is the other side of the contact wired to provide what the relay requires?

Poet.
  Reply With Quote
Old August 18th, 2018, 09:17 AM   #10
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
From what I was told it is supposed to be 0v at y7 the only way for me to get the contactor/relay to pull in is to add a wire from the negative on the 24V converter to the bottom of the contactor relay
  Reply With Quote
Old August 18th, 2018, 09:18 AM   #11
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
It has the 24v at the top just nothing at the bottom from y7
  Reply With Quote
Old August 18th, 2018, 09:33 AM   #12
goghie
Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 236
Greg,
I will write you some advices regarding your problem, but the first one would be to hire someone with more experience in PLC and wiring, because you can make more financial harm if you don't do.
If you don't want to employ someone else then you can try following:
If I remember good "COM2" is common for Y4, Y5, Y6, Y7, so first thing I would do would be to check is COM2 connected to 0VDC. If yes, I would check if COM2 and Y7 is closing when Y7 LED is ON. Is yes then I would check if COM2 is grounded. All this presuming that outputs are sinked...
  Reply With Quote
Old August 18th, 2018, 10:06 AM   #13
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
If I could hire someone that knows about this stuff I would but it's not up to me. So I am stuck trying to figure this stuff out. So that's why I am here to find some help with learning a bit more on how this stuff works and to learn how to trouble shoot it.


Like in the program when i monitor it most of the sensors have like timers in the program like one has T22 and when you put your hand over the sensors the 0 starts counting for a short period of time before it stops When I monitor Y007 that's on the wire that is connected to the bottom of the contractor I can see the sensors light up blue but the 0 on the timer I am guessing that's what the T22 is doesn't start counting like the rest do.
  Reply With Quote
Old August 18th, 2018, 10:17 AM   #14
goghie
Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 236
Why don't you attach the program? It would be much easier to help you.
  Reply With Quote
Old August 18th, 2018, 10:36 AM   #15
Greg7683
Member
United States

Greg7683 is offline
 
Join Date: Jun 2018
Location: Plainfield IN
Posts: 146
Here it is the one I am having trouble with is the 203 Run-in C Lift Because there is two programs in this link so the 203 program lol


https://1drv.ms/u/s!AqV1Z1yKcZ_3ghURVFVMuCsW_Pm4
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
photo eye delema BOWRIDER LIVE PLC Questions And Answers 4 October 22nd, 2004 12:43 AM


All times are GMT -5. The time now is 06:45 AM.


.