plc 115vac input

rick62

Lifetime Supporting Member
Join Date
Jul 2013
Location
tuscumbia al
Posts
45
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.
 
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.

What is that input coming from? Can the device you're monitoring create an inductive spike when it turns off? Can you use an interposing relay on that input?

A properly rated MOV in parallel with the input, and connected to ground may help.

-rpoet
 
Since we're talking about it, can anyone recommend a MOV or snubber they'd recommend to put across the coils?

I tried picking one out on Mouser a few weeks ago, but all the choices are overwhelming.
 

Similar Topics

Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
15
Hi All, Someone at work has put a PLC system on my desk, that's just been taken off an idle production line. He said "It's an S7 PLC. We don't...
Replies
3
Views
72
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
40
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
73
Back
Top Bottom