determining a program's size

ive been tasked, due to a restructure of our inventory, to find out how big our SLC programs are. specifically, we have several dozen 5/05s at our plant and we stock 16k, 32k, and 64k processors. I need to find out if 32k is big enough for everything and we will just stock a single 32.

I looked in controller properties and memory used and memory left doesn't add up. I think I am going at this wrong. How can I find out the "k" size of a given program?

thanks
  Reply With Quote
Old February 21st, 2018, 01:38 PM   #2
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,391
I think its just straight conversion... double click on the controller properties and you will see 'words used' and memory left, so memory left is 12xxx then you have 12k left

They are 16k 32k and 64k
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old February 21st, 2018, 02:13 PM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,732
There is some overhead that you can't count. I have a 32k SLC 5/05 and when I add up the "Instruction words used" "Data Table" and "Instruction Words Left" I get 29920.

I don't think there is a limit in the SLC on how you allocate available memory whether to data table or instructions like there is with some Micrologix models where you can only use a certain amount for data tables.

For your situation then, take the "fattest" SLC program you have and change processor types to the 32K, uncheck "Resize Data tables", verify program files, then check the controller properties. If you leave "Resize Data Files" it will shrink them for you to the last element used in each file which often can create a problem. If your verify fails due to a lack of space, manually shrink them as you choose, or do it again and let the software pare them down for you.

Be sure to leave at least 1k free at a bare minimum. Doing online edits can be a problem if you don't have enough unused edits.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

Last edited by OkiePC; February 21st, 2018 at 02:32 PM.
  Reply With Quote
Old February 21st, 2018, 02:21 PM   #4
merlin00724
Member
United States

merlin00724 is offline
 
Join Date: Oct 2007
Location: cincy, OH
Posts: 33
Perfect! Thank you very much
  Reply With Quote
Old February 21st, 2018, 10:26 PM   #5
Sydney
Supporting Member
United States

Sydney is offline
 
Join Date: Nov 2011
Location: Central Coast of California
Posts: 46
Quote:
Originally Posted by OkiePC View Post
For your situation then, take the "fattest" SLC program you have and change processor types to the 32K, uncheck "Resize Data tables", verify program files, then check the controller properties. If you leave "Resize Data Files" it will shrink them for you to the last element used in each file which often can create a problem.
Don't understand why AB allows "Resize Data Files" if it can create a problem. On several occasions we had to substitute processors with different memory sizes and had to decide whether to resize or not. I asked several Engineers over the years about this issue and know one could give me an answer. Just told me not to use unless absolutely necessary or verify program manually, can anyone elaborate.

Regards,
Sydney
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Naming ControlLogix / CompactLogix programs . Cydog LIVE PLC Questions And Answers 3 February 11th, 2018 08:54 AM
Off Topic: Rant about degree programs plc_user1973 LIVE PLC Questions And Answers 8 December 30th, 2009 11:09 AM
Can RSLinx upload ladder programs from PLC? noznoz LIVE PLC Questions And Answers 5 September 24th, 2007 01:16 AM
Determining PV+ 1000 datalog size for trends martyh LIVE PLC Questions And Answers 0 December 8th, 2004 12:23 PM
Conversion programs David_Emmerich LIVE PLC Questions And Answers 7 September 6th, 2002 05:57 AM


All times are GMT -5. The time now is 08:59 PM.


.