JackPW Member J Join Date Feb 2018 Location East Posts 15 Jan 15, 2019 #1 I'm extending the cable (to 100ft total) for an MTS temposonics transducer with Start/Stop output that will be in continuous flex. Would Continuous Flex rated Shielded CAT5E be a good choice here? seems like a good fit. Thanks
I'm extending the cable (to 100ft total) for an MTS temposonics transducer with Start/Stop output that will be in continuous flex. Would Continuous Flex rated Shielded CAT5E be a good choice here? seems like a good fit. Thanks
James Mcquade Member J Join Date Oct 2007 Location Nashville, Tennessee area Posts 3,676 Jan 17, 2019 #3 the additional 100 ft in length may require you to recalibrate the sensor input. james