What makes you think that? You are wrong. The voltage doesn't dictate the type of connection.magdyfayad said:yes , all you said i agree with you ,
but if we measured the voltage between the two hot wires at USA homes , it will be 240 VAC not 208 !! so the connection at USA homes not as figure c
magdyfayad said:as i think the connection at USA homes is a secondary for single phase transformer , but if the connection at USA homes is at figure c , then the secondary is for three phase transformer not single phase transformer !!
There is no such thing as a three phase transformer. The connection in figure C IS the way US homes are connected. It is single phase. Why are you concerned about the other 2 phases (A-B, C-A)? Why do you care that it's 3 phase? You are only using one of the 3 phases.
If I have 3 12 volt batteries in series, Someone could connect and get 36 volts. I can connect to just one of the batteries, and get 12 volts. I don't care what anybody else does with the other batteries. I'm only using 1 of the 3 phases.
Voltage doesn't dictate the connection. If you would study how a generator works, you would understand this. I guess you won't study, so I will continue to say the same thing over and over again in your 2 posts until you get it.
There is 2 types of 3 phase in the US that are close. 208/120 is 208 between phases. If I use any 2 wires, I will have single phase 208.
The other type is 120/240. It has 240 vac between phases. If I use any 2 wires, I will have single phase 240 VAC.
Magdyfayed: I want you to find a drawing of a DC generator. It will have one coil. It will have a magnet with a north and south pole turning on a shaft. I want you to explain the position of the magnet in relation to the coil at the 2 peaks of the sine wave and the zero crossing.