Communication S7-1200 over ISO TCP/IP with BEIJER HMI

Marcosbelgo

Member
Join Date
Jun 2015
Location
Belo Horizonte
Posts
34
Hi friends,

This is my first work with simatic and I am having some difficulties to comunicate S7 with HMI.

HMI: T5F-2 Beijer Electronics

S7 1200 1214C

I understood that to make this, I have to use T_CON. But, it is not clear for me.

Wich Is it nescessary blocks to estabilish communication, T_CON and T_SEND? wich parameters I have to set in these blocks? What is REQ????? What else I have to do in the TIA?

Bellow, I attached the screen configuration for HMI, what I put in src TSAP/rack dist/TSAP slot and link type (PG or OP)?


Thanks



Marcos

ScreenHunter_003.png
 
Haven't used that range of HMIs so this is all assumption. The HMI does have a Siemens driver so you shouldn't need to mess with any T_CON. Set Rack to 0, Slot to 1, Link Type as PG is fine, in the Beijer software. Make sure that the IP address is the one you used for the PLC. Check that it is part of the same group as the rest of the network settings for the HMI.

On the PLC, depending on which version of software, double click the picture of the PLC, under Profinet Interface / Ethernet Addresses make sure that you have the same IP address as set for the station on the PLC, and the subnet often 255.255.255.0 match the one used on the HMI. Then go all the way to the end of the list and find Protection and enable 'Permit Access with Put/Get.

Then test the system.
 
Just to add something to Bryans reply, in the S7 config under Protection & security, Connection mechanisms, there is a check box to permit access with PUT/GET. Some third party deevices need this checked.
 
Haven't used that range of HMIs so this is all assumption. The HMI does have a Siemens driver so you shouldn't need to mess with any T_CON. Set Rack to 0, Slot to 1, Link Type as PG is fine, in the Beijer software. Make sure that the IP address is the one you used for the PLC. Check that it is part of the same group as the rest of the network settings for the HMI.

On the PLC, depending on which version of software, double click the picture of the PLC, under Profinet Interface / Ethernet Addresses make sure that you have the same IP address as set for the station on the PLC, and the subnet often 255.255.255.0 match the one used on the HMI. Then go all the way to the end of the list and find Protection and enable 'Permit Access with Put/Get.

Then test the system.

Thanks friend, is exactly this, it works fine

Just to add something to Bryans reply, in the S7 config under Protection & security, Connection mechanisms, there is a check box to permit access with PUT/GET. Some third party deevices need this checked.

Hi Cottage, thanks!
 

Similar Topics

Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
43
Views
2,832
Which signals do I have to use to get data from camera. For example camera detects a defect and sends signal to controller. Power cable: CCB-PWRIO-05
Replies
1
Views
208
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
Replies
1
Views
379
Good day, everyone, We're trying to establish an S7 connection on ethernet between an S7-400 CPU and a new S7-1200 CPU (which is defined as slave...
Replies
10
Views
2,618
I don't have any prior experience with MicroLogix so the Communication Toggle Button is new to me. We currently have a few MicroLogix that are...
Replies
4
Views
2,208
Back
Top Bottom