Panelbuilder 32 error 3007

russrmartin

Member
Join Date
Aug 2002
Location
Eastman, Wisconsin
Posts
744
Hi guys. I have a panelbuilder 32 application which is giving me the error above when I try to download. The error says that the write tag is already in use. I am trying to change a value on two separate screens, so I am using the same write tage in the numeric entries. I'm also displaying the same read tag, and there is no error with this. Anyone have any ideas?
 
And 8 years later....

I found my error. I actually had 2 different objects with the same write tagname. I deleted the second and copied the first object to the second screen and all is ok now.

And eight years later, your response helped me fix the error that I was having.... I too had a set of two different objects with the same write tagname. I deleted one set of them, then just copied and pasted the other ones and the validation error is gone now.

Thanks!
 
How do we change it back to same object id for multiple screens? When I try to copy and paste it just go back to a different one.
 

Similar Topics

Hello, anyone had a similar experience? A customer has an old panelview600, it is faulted, but is communicating and they desperately need to...
Replies
8
Views
3,734
When trying to Upload from a Panelview 1000 I keep getting the following error message. Error [2158] DTL_E_DRIVER_NAME_INVALID Specified Driver...
Replies
3
Views
2,905
Error (2272)- PCCCSTS10, illegal command or format, including an old address. OK here's the scoop: I am making some requested changes for a...
Replies
1
Views
2,688
Hi all - Does anyone know if there's a decent way to import alarm text into a Panelbuilder32 file (v. 3.82)? I've already typed it once & don't...
Replies
5
Views
3,181
Hey guys. We have a couple of laptops that come up with the following error DBTemplate Copy Fail when trying to open a file. I have opened these...
Replies
6
Views
5,954
Back
Top Bottom