Hello all,

Im using modbus to communicate to an Omron 3G3RV drive. Im trying to use parameter A1-03 to initialize the parameters to the user initial parameters by writing 1110 to the register. Through the keypad of the drive it works fine. Does anybody know if there is a limitation that you cant initialiaze through communications?
 
A1-03 is usually done at the initial start up of the drive. After that most parameters are not changed. You have to store the "USER PARAMETERS" by setting 02-03 to 1 and the parameters are then saved as the "USER PARAMETERS". Maybe after you set 02-03 you might be able to then set A1-03 value to 1110 from the comms.

Why do you feel the need to initialize the drive to the user constants later on?

You can store the final setup program in the Key Pad via 03-01 and 03-02. Then if you modify constants for what ever reason, you can transfer the program from the key pad to the drive.
 

Similar Topics

is it possible to run more than one motor by using omron 3G3RV inverter? if yes how please?
Replies
2
Views
2,296
Hi There. I have PC to get few tags from PLC into C# windows forms application. What is the best and fastest way? I could not find Omron in...
Replies
3
Views
161
Our plant manger/my boss wants each line to display the takt time above the line. I am trying to research the cheapest way to do this. Our plant...
Replies
3
Views
166
Hello everyone. I am new when it comes to Omron PLCs. Currently I'm uploading program from CJ1M PLC using CS1W-CIF31 cable only. I connected the...
Replies
2
Views
98
Hello ! I am trying to use an omron cj2m-cpu33 with a CP1W-CIF01 plug in serial connector to talk to a zebra ZT610 printer. I am getting the data...
Replies
8
Views
316
Back
Top Bottom