Temperature Controls in a Glycol Chilling System

I'm starting on the controls of a set of glycol cooling vats this week. Something the customer wants is a centralized HMI to control and monitor all the vats, but he also wants to be able to set the temperature at the each vat. Each vat also has a roughly foot and a half deep threaded thermal well for a temperature sensor. My questions are two-fold.

I'm thinking of using a Type J RTD to monitor temperature. Is there any reason these will not work for this type of application?

I'm running into an issue with changing the temperature at the vats and at the HMI. I have to parallel them so that neither takes precedence in sending the data to the PLC. I was thinking of using a temperature controller to read the RTD and send a 4-20mA back out to the PLC, but the issue still remains with viewing and changing the setpoint from each individual station. Any suggestions on this?
  Reply With Quote
Old December 19th, 2017, 11:58 PM   #2
cjd1965
Member
United Kingdom

cjd1965 is offline
 
Join Date: Apr 2007
Location: UK
Posts: 1,543
Hi why not use 2 hmi screens that reference same tag and have the PID control in the PLC?

Most temperature controllers can have a remote setpoint function wherw 4 to 20mA sets the setpoint or even use comms like RS485 etc

I would strongly consider the multi hmi route though even if one is full blown and the local one is cheaper but factor in a PID faceplate with a trend as a mimimum standard
  Reply With Quote
Old December 20th, 2017, 01:16 AM   #3
willxfmr
Lifetime Supporting Member
United States

willxfmr is offline
 
Join Date: Nov 2013
Location: Wisconsin
Posts: 294
My first question would be what HMI software are you using FactoryTalk SE would make this pretty simple. Well... As easy as FactoryTalk makes anything else. But I agree with cjd1965. An HMI in a central location for monitoring, and as many as need to handle the local changes at the vats would be my first choice. Each HMI would be used to display information from, or give information to the PLC. All of the control programming should be handled in the PLC.

A type J thermocouple should work fine. If you want to bring the signal back as 4-20 you could use an RTD with a converter built into the unit. There may well be such a device for the thermocouple as well, but I'm not aware of one.

Bubba.
__________________
“Now will come the nay-sayers with all the reasons why you shouldn't do this. Some of them are teachers, and some of us are doers. Besides, you have got to let the smoke out of this equipment every now and then, or it starts to clog up the chimney.”
~Lancie1
  Reply With Quote
Old December 20th, 2017, 07:11 AM   #4
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 301
If there is a PLC already involved, and that PLC has PID and trending capability, you will have significant advantages to using the PLC for control. Both for the lower complexity of set point and display management as suggested by other posts, as well as readily available tools for tuning the control loops. It is likely the PLC has a better documented PID implementation than a low-cost off-the-shelf single loop controller (SLC). On the other hand, a SLC may have an auto-tune feature not available (or an expensive add-on) in the PLC. Though any auto-tune capability must be used with care on an important control loop.
  Reply With Quote
Old December 20th, 2017, 07:41 AM   #5
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,776
Quote:
Originally Posted by sparkie View Post
I'm thinking of using a Type J RTD to monitor temperature. Is there any reason these will not work for this type of application?
It will measure the temperature at the location of the thermowell, so the assumption is that the thermowell location is representative of the temperature of the entire bath.

A Type T thermocouple has better accuracy, out of the box, than a Type J and the Type T alloys are copper based, which are not subject to rusting, like the iron leg in a Type J.

A 3 wire RTD has better inherent accuracy than a thermocouple, using copper wire for connection between the element and the controller (instead of thermocouple extension wire), but you do have to pay attention to which wire goes where when connecting it to an input. RTD's do cost slightly more than thermocouples.

Temperature elements used in thermowells should be 'spring-loaded', so that the element tip is forced against the thermowell by spring pressure. And it pays to use some thermal conductive grease to aid thermal conduction. You measure the bore depth to get the right length spring-loaded element.
  Reply With Quote
Old December 20th, 2017, 10:24 AM   #6
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 301
+1 to danw post.

Unless you have a large number of thermocouples, you will probably be better off with signal conditioners (TC mV to 4- 20 ma) at the device instead of long runs of extension wire with potential wiring errors (e.g., uncompensated terminals, inadvertent cold junctions) going to thermocouple inputs on the PLC or SLC.

For cold temperature measurement we always use RTDs for accuracy and stability.
  Reply With Quote
Old December 25th, 2017, 05:42 PM   #7
sparkie
Lifetime Supporting Member
United States

sparkie is online now
 
Join Date: Nov 2014
Location: KS
Posts: 733
Thanks for the info guys. I'll be going with spring-loaded RTD's and I'm going to use panelmeters for the temperature display and signal conditioning. I'm going to try to talk him out of temperature adjustments at each station, as the control panel for temps is less than 50 feet away.
  Reply With Quote
Old December 25th, 2017, 08:01 PM   #8
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 860
I don't see the issue with multiple HMIs? They can all reference the same setpoint without conflict.
  Reply With Quote
Old December 26th, 2017, 12:48 AM   #9
sparkie
Lifetime Supporting Member
United States

sparkie is online now
 
Join Date: Nov 2014
Location: KS
Posts: 733
Quote:
Originally Posted by Saffa View Post
I don't see the issue with multiple HMIs? They can all reference the same setpoint without conflict.
The issue is cost. 14 small HMI's would add up to quite a bit. When I asked what all this equipment needed to do, I was me with "I want it to make my coffee for me." Of course, if money is no problem then a coffee making function is no problem either .
  Reply With Quote
Old December 26th, 2017, 04:51 AM   #10
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 860
Ok, 14 is a bit excessive!

I think red lion's HMIs have a web interface version... chuck in a Wifi access point and give them any ipad as their mobile HMI.

I think some of the new Magelis panels can do the same but we don't ever make use of this feature so not sure.
  Reply With Quote
Old December 26th, 2017, 06:36 AM   #11
Pete.S.
Member
United States

Pete.S. is offline
 
Join Date: Mar 2016
Location: Fl
Posts: 457
I'd go for small HMIs for sure. There are small simple HMIs that are in the price range $100 to $200.

14 x $100 is $1400 so it's not a huge investment I think.

Last edited by Pete.S.; December 26th, 2017 at 06:43 AM.
  Reply With Quote
Old December 26th, 2017, 08:01 AM   #12
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 157
Are you aware of the existence of Single Loop Controllers ("SLC" -- not to be confused with the AB PLC with the same initials) ?

These cheap gizmos (~$100) do all the PID control for you, and have a display where the setpoints can be entered and temperature monitored. They also have communication capability (typically RS485 modbus) to talk to/from PLCs.

Your PLC would thus not need ANY AI/RTD or AO cards to talk to the thermocouples and glycol control valves, just a Prosoft module to talk to these guys. I think this is the kind of solution that your customer is expecting from you -- local control at the vat's; supervisory control at the HMI.

Technically / in theory you don't even need a PLC -- an open-source HMI like the AdvanceHMI that's popular on this site could do the Modbus interfacing with the SLCs. I've seen this sort of thing done; whether it's a good idea or not depends on one's ability to service/troubleshoot it down the road.

Anyway, just throwing it out there. Generally speaking, telling a client that he shouldn't want what he wants (local control) isn't a great way to get that client to come back to you. It's easier to keep clients than find new ones.

Good luck!
  Reply With Quote
Old December 26th, 2017, 08:31 AM   #13
Pete.S.
Member
United States

Pete.S. is offline
 
Join Date: Mar 2016
Location: Fl
Posts: 457
Quote:
Originally Posted by Aardwizz View Post
Are you aware of the existence of Single Loop Controllers ("SLC" -- not to be confused with the AB PLC with the same initials) ?

These cheap gizmos (~$100) do all the PID control for you, and have a display where the setpoints can be entered and temperature monitored. They also have communication capability (typically RS485 modbus) to talk to/from PLCs.

Your PLC would thus not need ANY AI/RTD or AO cards to talk to the thermocouples and glycol control valves, just a Prosoft module to talk to these guys. I think this is the kind of solution that your customer is expecting from you -- local control at the vat's; supervisory control at the HMI.

Technically / in theory you don't even need a PLC -- an open-source HMI like the AdvanceHMI that's popular on this site could do the Modbus interfacing with the SLCs. I've seen this sort of thing done; whether it's a good idea or not depends on one's ability to service/troubleshoot it down the road.

Anyway, just throwing it out there. Generally speaking, telling a client that he shouldn't want what he wants (local control) isn't a great way to get that client to come back to you. It's easier to keep clients than find new ones.

Good luck!
If all the client want to do locally is to change the setpoint then I think your solution is the best.

If modbus is fully implemented in the loop controller you could read and write all setpoints, process values, PID tuning/settings, operation mode etc from the PLC/HMI. That also means you can do full trends on the HMI if you read the SP/PV/OP trifecta on a regular basis.

Also good from a cost and installation point of view since you would wire up everything to the loop controller so there is a minimum of wires to run.
  Reply With Quote
Old December 27th, 2017, 04:24 PM   #14
sparkie
Lifetime Supporting Member
United States

sparkie is online now
 
Join Date: Nov 2014
Location: KS
Posts: 733
Thanks for all the input. I was actually playing with advancedHMI and the Logix simulators, but getting it to talk to them is quite a pain, so I wasn't really able to mess with it too much. Plus, with all of the stuff he wants to do with data I think a paid package would be preferable.

As far as using PID controllers for each individual VAT, it is a nice option indeed, especially since I'm going to use a PID controller for temp display anyway, and as mentioned before, I don't even really need the PLC. All of the logic can be done in the SCADA for cycle times and such, however there will also be glycol chiller monitoring and integration as well, plus I'm so sure that he will find other things he wants to add as time goes on I would rather just do the logic in the PLC.

It is excellent advice to refrain from "telling a customer what he needs," and it is okay to make suggestions based on your experience as to what may work well for a customer. I think the fact that the longest distance between a vat and the control panel is less than 50 feet, and that the customer will also have mobile access to the HMI on his cell phone is a good reason to refrain from having local controls, but once again, if it is something that he really wants it is something I'm more than willing to do.

Lots of design decisions to be made here, and I'm grateful for all of the input.
  Reply With Quote
Old January 4th, 2018, 01:31 PM   #15
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,633
I control this type of temperatures in holds of ships, with pretty simple Single Loop controls, they have everything inside one unit, complete with display, and are pretty cheap, They can have a communication like modbus or even etehrnet
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Cooling Tower Temperature and Vacuum Control daniyal LIVE PLC Questions And Answers 4 January 17th, 2013 03:25 PM
Is a PLC the right way to go in this case? Fasthotrod LIVE PLC Questions And Answers 30 November 2nd, 2007 12:31 PM
Eurotherm controls 2500 I/O system Uno LIVE PLC Questions And Answers 0 August 11th, 2003 12:34 AM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 10:57 AM


All times are GMT -5. The time now is 10:46 AM.


.