Cooling Tower Temperature and Vacuum Control

Dear All,

Its being very tough for me to control the cooling water temperature and vacuum by PID loop. attached is the control routine which i am using to control the temperature an Vacuum.
The system is consist of 8 cells of Cooling tower Fans in Power Plant that is operation by 8 PF755 VFD's by increasing and decreasing the speed of all drives at same time with PID controller to control the Elements.
Normally Vacuum Controller activated when the temperature is greater the Setpoint, and when the temperature is below down to the setpoint the control switches over to the temperature controller and decreasing the speeds to achieve the setpoint. But the fan speed decreases untill the temperature does not reached at the setpoint and it makes the oscillation for the drives. I have tuned the PID loop on very slow response to stable the speed at which temperature again rise but temperature goes down very rapidly.
Kindly tell me is there any better and accurate way for controlling or it need to be tune it again for nullify the oscillation and smooth the controlling.

Looking forward for your kind response
Thanks
Attached Images
File Type: jpg PID.jpg (39.6 KB, 51 views)
Attached Files
File Type: zip Control_Routine.zip (10.8 KB, 19 views)
  Reply With Quote
Old January 17th, 2013, 07:17 AM   #2
daniyal
Member
Canada

daniyal is offline
 
daniyal's Avatar
 
Join Date: Nov 2007
Location: Mississauga, ONT
Posts: 51
Nobody have the Answer
  Reply With Quote
Old January 17th, 2013, 07:37 AM   #3
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,642
please give a nice diagram and what type of control you are using.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Old January 17th, 2013, 09:07 AM   #4
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,904
This is one of those broad, open ended questions that are almost impossible to answer on a forum like this:

We don't know what the physical system looks like - all cooling towers aren't the same

You don't identify if the problem occurs all of the time, or only at extremes of loading or ambient temperature

You don't identify if all of the towers have this problem, or only some.

You don't tell us how tight you want to control the temp or how tight you need to control the temp

You don't tell us why you want to use a single PID loop to control what are probably not 100% identical towers in terms of performance, water distribution etc.

And, personally, I wouldn't use PID for this.

Remember, the guys on this forum get paid to do what you are asking them to do for nothing. They are helpful, but there is a limit to how much time they can and should devote to a problem you are probably getting paid to solve!

It doesn't help to post snarky comments like "Nobody have the Answer" either. (Especially if you can't be bothered to check your grammar!)

Last edited by Tom Jenkins; January 17th, 2013 at 09:20 AM.
  Reply With Quote
Old January 17th, 2013, 03:25 PM   #5
jandrul
Member
United States

jandrul is offline
 
Join Date: Jan 2013
Location: NY
Posts: 6
Here are some ideas:

(1) Sounds like there maybe a discontinuity transitioning from temperature to vacuum control. The process dynamics may be radically different when the vacuum comes on. Try to decouple this by turning on the vacuum control a little later say when T > Tsp by 5 degrees. This will give temperature control more time to catch a disturbance.

(2) Tuning of Temperature loops is difficult. The process is often 2nd order with considerable deadtime. If you have any PV filtering take it out, you don't need it with temperature. For temperature loops, the P&I parameters are much less aggressive then typical defaults often having a controller gain of .1 or less and having 3 to 5 minutes between repeats.

(3) This process is relatively non-linear particularly at the dew point. You may have a high degree of interaction with Pressure and temperature ( I refer to some dew point tables ). See if you can operate on linear part of the curve(s). Otherwise it could be very sensitive and often difficult to control.

(4) Could be your process gain is too high ? Try staging the start of your fans to lower process gain.


Hopefully this helps. Like Tom said we obviously need the whole picture here. I recommend that you hire an expert in cooling tower control to audit your system.



John
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Temperature control tgaljar LIVE PLC Questions And Answers 24 December 31st, 2008 12:01 PM
Vacuum thermocouple integration to PLC grignon LIVE PLC Questions And Answers 1 April 26th, 2003 07:58 AM


All times are GMT -5. The time now is 08:45 PM.


.