Omron CQM1 High Speed Counter options.

Mr_B

Member
Join Date
May 2005
Posts
79
If u configure an Omron CQM1 PLC to use the High Speed Counter Incrementing only with a Software reset meaning you will use Input 0.4 for the pulses. Will this mean that input 0.5 and 0.6 can be used as normal inputs?
 
Mr_B,

Reference Omron Manual W228-E3-2, Page 36.
"If only the software reset is to be used, terminal 6 can be used as an ordinary input. When in Incrementing Mode, terminal 5 can be used as an ordinary input."

Hope this will help.
 