Puzzling Question About Honeywll UV Scanner Module

Russ

Lifetime Supporting Member
Join Date
Jun 2002
Location
Ohio.. Go Bucks!!!!
Posts
261
I have a honeywell purple peeper at a clients site and noticed an issue about eight months ago. The relay module (ST 7800 A 1039 /9645) wouldn't always initiate the pilot during start up. The LED for the pilot wouldn't always turn on (on the module), and when it failed to turn on I'd get a fault once the pilot timer completed. This weird condition only happened during start up. Once the burner was lit there were no further odd behaviors.
This lighting issue could happen upwards of a dozen times in a row then disappear for another dozen lights. At the time once the burner was lit, it stayed on. I noted the issue, and recommended troubleshooting the cause with the likely possibility of having to replace the module.

However, about six months ago I added a utility savings program to the equipment. This required the burner to be turned off on a daily basis. I got my chance to troubleshoot.
When troubleshooting the module issue, I noticed leakage voltage, and believed that was possibly a factor in the pilot issue. I connected the keyboard display module (S7800 1001) to verify the exact sequence of events and found that once connected the relay module worked perfectly. The load the keyboard module added seemed to offset the effects of the leakage voltage. There were no further pilot issues. It lit every time. Before connecting the keyboard module I was going to recommend replacing the main relay module.
Every morning the unit automatically lights off, and for the past six plus months there hasn't been a single flame failure.


Why?
 
Last edited:
1) Which model (RM78xx) relay module?

2) Did it complete the purge?

3) When the purge finished, did either terminal 8 or 10 engergize? Presumably not.

4) Did you check the fault code history with a keyboard display?
 
It sounds to me as though it may be related to the strength of the pilot and/or the scanner's ability to see the pilot. What type of burner is it on? In thousands of burner and boiler start-ups, I have seen a lot of strange Honeywell FSG behavior but never a leakage current on the scanner.
 

Similar Topics

We have an inductive sensor mounted in front of a rotating pulley, which has one small steel part rising close to the sensor. The sensor is wired...
Replies
9
Views
2,211
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
106
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
0
Views
51
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
79
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
80
Back
Top Bottom