I have a panelview plus 7, that runs on version 10 firmware. I am trying to run an application from factorytalk view that has version 8 firmware. but the panelview will not accept my run time application. It says the firmware is incompatible. What can I do?... I tried down grading panelview to version 8 but it wont work.
 
First off there are two (2) models of the PVP 7 - Standard and Performance.
Which one are you working with?
I would check the Project Settings and be sure to select the PVP 7 "Execute MER on PanelView Plus 7 (Standard) or (Performance) you are using.

Also apply the latest RA patch roll-ups CPR9 SRx it is required for FTV ME version 8.0 and later to fully support PVP 7 standard terminals.

Techconnect RA KB 685965
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/685965
 

Similar Topics

I've adjusted the IP of the Panelview Plus as well as the DNS servers; the screen does not show up in the search when I go to the transfer utility...
Replies
3
Views
105
Replaced overlay and glass in HMI but now I can not calibrate the touch screen any suggestions.
Replies
1
Views
84
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
89
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
146
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
125
Back
Top Bottom