+1 for flow switches (sail switch, paddle switch etc.). ULTIMATELY, what you want to know is if the fan is blowing air. The motor could be running just fine, but the shaft or belt broke. Once you know there is no air flow, you alert maintenance to go find out why.
If you are wanting to do it with electrical sensing of the motor, spend a little extra to get something that monitor kW, not just current. Current fluctuates with voltage, kW is ONLY associated with the actual load on the motor. So a current sensor may be satisfied by the motor current of a blocked fan because it sees active and reactive current as the same, a kW sensor would see the low PF to know that the load drop off too low.
If you are wanting to do it with electrical sensing of the motor, spend a little extra to get something that monitor kW, not just current. Current fluctuates with voltage, kW is ONLY associated with the actual load on the motor. So a current sensor may be satisfied by the motor current of a blocked fan because it sees active and reactive current as the same, a kW sensor would see the low PF to know that the load drop off too low.