Siemens 1517F-3 and Redlion DSPZR Communication issue

telos

Member
Join Date
Aug 2017
Location
USA
Posts
4
The Physical Details:
Network 1: Rockwell
- EN2T 192.168.1.102
- Red Lion Built in Ethernet port 192.168.1.125
- Rockwell VM - 192.168.1.247
-- all subnet 255.255.255.0
-- Gateways 0.0.0.0
--- Everything pings fine and get data in local tags in Crimson

Network 2: Siemens
- Onboard port X1PR1 - 192.168.0.1
- Redlion Expansion port 192.168.0.20
- Siemens VM 192.168.0.223
-- all subnet 255.255.255.0
-- Gateways 0.0.0.0
--- Everything pings fine Get N/A in Value when looking at online value in Crimson.

I set up a program in the G3 HMI to ping the Siemens PLC from the Redlion. This returns successful.

The only documentation on Red Lion's website says you need to disable protection (set to full access), enable PUT/GET and disable Optimized block addressing. I have done those 3 things. Red Lion tech support was stumped.

Any Ideas?
 
Siemens S7 TCP/IP Master with TIA S7 Tag Import.

Red Lion tech support confirmed that is the only TCP/IP one that will work with the 15xx processors.

We've thought of adding the profibus card to the red lion but that is the nuclear option at this point...
 
Siemens S7 TCP/IP Master with TIA S7 Tag Import.

Red Lion tech support confirmed that is the only TCP/IP one that will work with the 15xx processors.

We've thought of adding the profibus card to the red lion but that is the nuclear option at this point...

How are the tags imported? is it an online import or an offline import?

Are you addressing the tags by their tag name, or by their DB number and address?
 

Similar Topics

I have established an online connection to a machine using an S314 processor. I am using an mpi connector and simatic manager. The online...
Replies
2
Views
33
Hi everyone, i have a Siemens S7-300 Cpu 314C-2 DP with several cards of i/o and servos my laptop has TIA version 16 and 17 loaded and...
Replies
4
Views
132
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
211
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
27
Views
561
Hi everyone, I am an omron plc tec , lately I came across a siemens s7 200 cn plc . Can someone help me regarding the software required and...
Replies
26
Views
496
Back